Anonymous Poster

Thermocouple

04/20/2010 1:59 AM

how to calculate degree centigrades to millivolts it belongs to thermocouple if 165degree what will be the output of thermocouple

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#1

Re: thermocouple

04/20/2010 2:16 AM

Depends on what type of thermocouple you're using. Also whether that's degrees celcius or fahrenheit. Here's a start :

http://www.claustemp.com/an-htp15.htm

__________________
Charlie don't surf.
Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: Thermocouple

04/20/2010 6:38 PM

Is the gradient, from hot end to cold end, across the thermocouple = 165°C?

Or is the hot end at 165°C and the cold end at some other temperature?

What is the cold end temperature of the thermocouple?

What type thermocouple?

Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#3

Re: Thermocouple

05/23/2010 6:05 AM

Tables are your friend, as Steve has pointed out. But it's useful to remember the number 40mV per degree C, for a quick estimate. Most types are in that territory at room temperature, decreasing at very low temps, increasing somewhat at high temps.

__________________
Thanks, Win
Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#4

Re: Thermocouple

05/23/2010 3:20 PM

The thermocouple (T/C) tables are valid only when the cold end is ice point or cold junction referenced.

The T/C tables do not provide a direct value when the 'cold' end is at any temperature other than 0°C, or when ice point or cold junction compensation is not implemented.

For instance, take a type K thermocouple lying on a bench top at an ambient temperature of 30°C. The temperature of both ends of the T/C is identical at 30.0°C.

A thermocouple table gives a value of 1.203mV for 30.0°C. But measuring the output of the T/C will give a reading of 0.0mV, because there is no thermal gradient across the thermocouple, even though the 'hot' end is at 30°C.

The temperature of the cold end junction point must be added to the uncompensated temperature value read from a mV table.

Reply Score 1 for Good Answer
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Carl_E (2); stevem (1); Winfield Hill (1)

Previous in Forum: Instrument Cable   Next in Forum: 12VDC discharge time thru an inverter to a 1.5AC load

Advertisement