Advice for Circuit Design for Cafeteria

04/20/2010 2:31 AM

Dear Engineers good day for all of you,

I'm working in a project for designing a panelboard for new devices required to be added in a cafeteria. The below table shows the new devices will be used in a cafeteria with their ampere rating.

1Dishwasher42A
2Boiler dishwasher68 A
3Booster80 A
4Rice Cooker47.2 A
5Oven 2 NO.88 A
6Water Heater40 a
7Meat Cutter50 A
Total Required load @220 3PH.415.2 A

I suggested to use near substation and we will take the supply from the "Main Bus" as it illustrated in the picture below the total full load current (A) on this bus is 750.56A, where we find the existing full load = 367kVA.

Regarding of previous calculation I calculated the total current of the new devices which is 415.2A. In addition, if the voltage supply is 220V the Load will be equal 91.344kVA.

Accordingly, I designed single line diagram including circuit breakers and transformer

Please, check the single line diagram attached and the rating of the CB and Transformer, and tell me if I'm in a right way of my calculation and design or it is need for some correction.

__________________
Do not despair, success comes after several attempts that failed
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Need your advice for a circuit design

04/20/2010 3:26 AM

Because of the second 80A oven, the total connected new load is 503.2A, rather than 415.2A. However, if both ovens do not operate at the same time, or other diversity factors apply, you may be able to design for less than 503.2A.

After this is clarified, there will be some other things to recheck.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: Need your advice for a circuit design

04/20/2010 5:46 AM

1) Consider the ampere rating of second oven

2) consider ampere rating of the spares

3) calculate total load current

4) calculate required kva of transformer based on ur sec. voltage and load current

5) choose the transformer accordingly

6) calculate primary current of transformer

7) select protective device for transformer based on tht calculation......(since its a step down transformer your primary current will be smaller thn secondary)...

__________________
shamith gambhir, electrical engineer
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2009
Posts: 15
#3

Re: Need your advice for a circuit design

04/20/2010 8:20 AM

thanks engeneers,

Ok if there is one oven only will be operated at 88A and we keep the total current load = 415.2A. If 40% spare will be added wich it means 166.08A spare so the total current will be 581.28A, I will choose here 630A main circuit breaker for the circuit. Moreover, with the voltage = 277V the load will equil = 581.28A X 277V= 161kVA. Accordingly, I proposed 225kVA transformer 480/277V. at this step I need to determine the CB for the primary side of transformer and install this CB in a main distribution panel which is already loaded with 750.56A and the load = 360kVA. However, I choos 800A CB but I'm not sure if it appropriate CB or not.

Please advice how can I calculate for the primary CB

__________________
Do not despair, success comes after several attempts that failed
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#4

Re: Advice for Circuit Design for Cafeteria

04/20/2010 8:26 AM

i forgot to mention..........while calculating take care abt the inrush current in transformers.......i think watever u ve chosen is correct jus consider above mentioned points......if possible provide a differential protection for the transformer which has to overcome transformer inrush current............

__________________
shamith gambhir, electrical engineer
Register to Reply
Participant

Join Date: Apr 2010
Posts: 2
#5

Re: Advice for Circuit Design for Cafeteria

04/20/2010 8:55 AM

If the load amperes you have indicated for each of the listed loads are 3 phase loads you have indeed a big group of cafeteria equipment load. I guess not all of your loads indicated are 3 phase equipment. Some are probably single phase. In that case you have to balance your loads in each of the phase in your panelboard. You will realize that if you do it correctly you will end up with a much smaller total ampere load and KVA of course). Also when calculating the transformer kva size, it is based on the total demand load which is less than the total connected load. Not all the equipment operate at 100% demand at the same time.

harmonic filter

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#6
In reply to #5

Re: Advice for Circuit Design for Cafeteria

04/20/2010 9:29 AM

Good points harmonicfilter, the numbers on face value imply such an enormous load that I wonder about their origin. This is not a difficult engineering task once one knows the real values involved. This leads me to two conclusions that I cannot decide which is true. Either this is a student's homework problem or somebody doesn't understand a proposed or a working design's electrical loading/budget configuration.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7

Re: Advice for Circuit Design for Cafeteria

04/20/2010 10:36 AM

If I am not mistaken, NEC requires that you list and accomodate the nameplate FLA of every device in the circuit. You cannot assume that some equipment will not be operating when sizing service.

But then, we don't know where this is, and I am NOT an electrical engineer.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Advice for Circuit Design for Cafeteria

04/20/2010 11:50 AM

At the bottom of your table you list "Total Req Load @220 V @3PH 415 A"

220 V X 415 A X 1.73 = 158 KVA and not 91 KVA. If you add 40% to this figure you would have 158 KVA x 1.4 = 221 kva and 581 amps.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2009
Posts: 15
#9

Re: Advice for Circuit Design for Cafeteria

04/21/2010 1:47 AM

Thanks all,

Eng. wareagle, thanks for your correction and regarding of the new values we still can use the same rating of main CB 600A and for the transformer load we can use same chosen rating load 225kVA or we can go with 300kVA.

Moreover, Eng. SHAMITHGAMBHIR1 gave a good point which is inrush current for the transformer where I couldn't till now know how to get it, (I need help if anyone can tell me how to get it).

According to Branches CB poles I proposed 1P for all breakers.

__________________
Do not despair, success comes after several attempts that failed
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: Advice for Circuit Design for Cafeteria

04/21/2010 9:19 AM

Sorry to say the following:

You are not qualified to work this out! Please consult an electrical engineer whose job is designing power circuits to supply such installation. It is dangerous, both for your costing and safety to try and work this out withut the proper knowledge! The amount of load you mentioned is too great for just an amateur to handle!

Please be wise and not foolish to attempt this exercise: No one can help you remotely when you are confusing the amps and the phases...etc...Inrush current etc...

Good luck!?

Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 15
#12
In reply to #10

Re: Advice for Circuit Design for Cafeteria

04/24/2010 1:15 AM

thank you for your view, I appreciate. However, I think you have a good knowledge to share it with us better than estimating my qualification.

hope to concentrate on the main query

__________________
Do not despair, success comes after several attempts that failed
Register to Reply
Power-User

Join Date: May 2008
Location: Ottawa Ontario Canada
Posts: 128
Good Answers: 6
#11

Re: Advice for Circuit Design for Cafeteria

04/21/2010 7:16 PM

I spent 10 years as a commercial appliance tech. and would suggest to the owner that he purchase a LOW TEMP. dishwasher that uses a chemical based sanitizer and not hot water . This would save approx. 150 amps. The unit cost is less than half of a booster type unit and is much better all around .? Or he could lease the system like everyone else does.?

He should also go with a gas water heater .?

Dont get this .

__________________
What dosent kill you makes you stronger , lifes a trip so sit back and try to enjoy the nice scenery.
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

harmonicfilter (1); LAA_Lucke (1); lyn (1); machine head (1); megatron (3); redfred (1); SHAMITHGAMBHIR1 (2); Tornado (1); wareagle (1)

Previous in Forum: Induction Motor Traction Drive   Next in Forum: electrical energy audit of chick hatchery

Advertisement