Autosynchronization of Hydro Plant

04/20/2010 5:44 PM

We tried Autosync of an old diesel start gas plant with settings like 0.5 Hz/s characteristics, 0.25s pulse, 10s pulse interval for frequency control and it worked ok.

How different is a hydro plant in terms of settings? Could I use the same settings? We couldn't obtain the characteristics from both the plants as it is pretty old.

Also does autosynchronization require supervision like contact close or is ok to close the breaker automatically without supervision once Autosync is started , which of these is normally used in the field?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Autosynchronization of Hydro Plant

04/22/2010 12:00 AM

I am not an expert on this, but since no one else has chimed in yet, I will make a suggestion. Gensets are typically higher speed, lower mass, with lower rotational inertia. They, along with their governors, are thus quick in responding to load variations (short time constant). On the other hand, hydro turbines are slower, heavier, and higher in rotational inertia. Thus they will not react so quickly to load changes (longer time constant). This will affect the tuning of control loops.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Good Answer
Commentator

Join Date: Nov 2009
Location: PA
Posts: 83
Good Answers: 1
#2
In reply to #1

Re: Autosynchronization of Hydro Plant

04/23/2010 11:14 AM

The hydro plant has this butterfly valve and a vertical motor to open and close the water. In our design the pulse width for raise and lower frequency is same assuming the system is linear, it worked fine with gas turbine but in hydro the motor does more work to close the gate against water and less work to open so for the same pulse width ,the change in speed is different for raise and lower.
2. Is this the way all Hydro plant works with different characteristics for raise and lower? This plant is 87 years old with old system.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Autosynchronization of Hydro Plant

04/23/2010 11:00 PM

It sounds as though the speed of whatever drives the valve is influenced by the load. What type of drive system is it?

Can you set different pulse rates/widths for opening versus closing?

Interesting problem. I'm not too familiar with hydro specifics, so this is all conceptual generalities from me.