Anonymous Poster

Megger Test

04/26/2010 2:14 AM

hi,

would you please help me on this as i am new on electricial training,

when i want to test the insulation for electric motor or generator, how much is the minimum reading to say it is not grounded? is it right to say it should not be less than 1Mohms?

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#1

Re: megger test

04/26/2010 2:28 AM

No. 1Mohm is quite low. When I test the motors etc with my megger by passing 1000V, the reading is 10-200Mohems which we consider ok. 1Mohm mean some problem.

__________________
Don't assume any thing, always check/ask and clear yourself
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Megger Test

04/26/2010 11:41 AM

While 1 megaohms is certainly not an indisputable good insulation value, I would say that it now depends on the application in question to say this passes or fails. If your motor/generator has for a normal operating range 12V @ 500A then this leakage current would be considered negligible.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster
#3
In reply to #2

Re: Megger Test

04/27/2010 12:29 AM

hi,

so you mean to say that every motor has defferent value which determine if its ok or not, depending on how many voltage and how many amps going through that motor/generator winding?

thanks

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4
In reply to #3

Re: Megger Test

04/27/2010 9:48 AM

Of course. Doesn't everything have a sliding scale that depends on circumstance.

If you had asked instead which is stronger, a black ant or a human Olympic weight lifter? The only true answer is it depends on how you define strength. If you go by solely the total amount of mass each can lift uninjured then clearly the much more massive Olympian wins. But if you consider strength across species as a percent of body mass each can lift, then by just as overwhelming a margin the ant wins.

It's always a matter of perspective.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Participant

Join Date: Jun 2007
Location: Michigan
Posts: 3
#5

Re: Megger Test

04/30/2010 12:52 PM

The best way to test the insulation of a motor is to perform a Polarization Index, 10/1 Minute Ratio. To do this you will need to megg the motor for ten minutes, record the ohms at 1 minute and then again at 10 minutes. Do this for all phases of the motor. If the results are less than 1, Insulation Condition is Dangerous. 1 to 2, Insulation Condition is Questionable, 2 to 4 Insulation Condition is Good, Above 4 Insulation Condition is Excellent.

__________________
The grass in not greener on the other side. Its just a reflection of the grass you are standing in.
Reply