Column Deviation From its Position

04/27/2010 5:44 AM

Dear engineer.

I need your advise on deviation of column from its position.

It happen contractor setup columns out of its position by 75mm in which if allowed to proceed will protude out the wall by 75mm because it flashing with the wall in outside and if we need to return to the required position all reinforcements are supposed to be cranking in one direction which is not recommended in codes of practice because of buckling effects.

Please advise in the situation like this what we supposed to do?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Column Deviation from its position

04/27/2010 6:58 AM

Who made the mistake?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#2
In reply to #1

Re: Column Deviation from its position

04/27/2010 7:02 AM

Wasn't me

__________________
health warning: These posts may contain traces of nut.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#6
In reply to #1

Re: Column Deviation From Its Position

04/27/2010 10:32 PM

Would knowing make the answer to the question easier?

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7
In reply to #6

Re: Column Deviation from its position

04/28/2010 6:43 AM

Yes. Please follow the link in Del's post #4

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Participant

Join Date: Apr 2010
Posts: 3
#10
In reply to #1

Re: Column Deviation from its position

04/28/2010 12:35 PM

Contractor made mistake then need attention of consultant

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#11
In reply to #10

Re: Column Deviation from its position

04/28/2010 6:07 PM

"Contractor made mistake ..." - then it's the contractor's responsibility to fix it.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Anonymous Poster
#3

Re: Column Deviation from its position

04/27/2010 7:26 AM

Rip it out and replace it.

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4

Re: Column Deviation from its position

04/27/2010 7:35 AM

It's a bit like this thread...
If all else fails, try doing it to the spec.
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5

Re: Column Deviation From its Position

04/27/2010 12:47 PM

Let it protrude 75 mm ( if its not in your neighbours land). adjust column section for added span of 75mm.

usual disclaimer applied.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8

Re: Column Deviation From its Position

04/28/2010 10:09 AM

You might begin by telling us how big the column is.

Does the 75mm represent 1% of the column dimension or 75% of the column dimension?

Register to Reply
Participant

Join Date: Apr 2010
Posts: 3
#9
In reply to #8

Re: Column Deviation From its Position

04/28/2010 12:30 PM

Column size is 500X500 and column was supposed to set up at the centerline of gridline .Now is out of position by the deviating of 75 mm.This is at Raft foundation level.What is the way forward to correct problrm like that.

Best regards.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 270
Good Answers: 19
#12

Re: Column Deviation From its Position

04/29/2010 3:35 AM

Given the information provided so far:

- 75mm out of tolerance

- 500x500 post

- raft foundation

Can I assume the following:

- you have a +/-20mm positional tolerance in your spec for the position of columns

- the raft foundation has either shear rails or shear links and also has a local thickening at the post position to take the shear around the post

- it is a raft foundation and your post is probably designed as a simply supported post with no moment connection to the raft (unless you have done so specifically)

- your post is designed with probably about 3%-4% steel reinforcement (although it is the lowest post in the structure)

- a 500x500 post makes it sound like a 6 storey building (this is a hazardous guess but given that you have come to this forum, I assume that you are not talking of a very important building)

Advice is:

- it is the contractor's error and in your spec you have clauses that say that the contractor is to propose a solution for the consultant's approval

- the contractor should employ an engineer to show how he is going to rectify things so that they are the same as the architect originally intended

Practically this amounts to:

- reducing the size of the column (by about 50mm on one side out of the 500mm post) and perhaps installing some additional re-bar by drilling in chemically bonded re-bar e.g. resin anchors as deep as the raft allows

- decrease one dimension and increase the other so that it is now 450x550

- increasing the concrete strength for the post concerned from say RC40 to RC50

- getting calculations from the contractor which show that the proposed new set-up works

__________________
omw7
Register to Reply