Hi All,
Can someone give me knowledge about power transformer or auto transformer protection according to impedance?
What are the advantages?
Do you know where can I find documentation about this?
Thanks.
Either exist as you are or be as you look. Rumi
Re: Transformer Protection - 'According to Impedance'
05/01/2010 2:02 AM
It is mainly for short circuit protection(other incidental advantages may be available at times).SC protection with inst.o/c element is set generally a little above through fault current.As such fault coverage is variable depending up on source impedance.For some systems it may become critical and in extreme cases there is a risk of fault remaining undetected by the inst. element. With the distance protection , in principle,this anomaly is eliminated since it can be set to have definite reach irrespective of source impedance.The main dis advantage is the measurement is complex and voltage dependent.Hence usually numerical o/c relay is specially configured for adequate coverage in all conditions.We usually give numerical relay oc protection and back it up by a distance relay when essential. Like any protection topic this will also require specific check in each instance.
Better not count the cent if the risk is many many dollars.
05/04/2010 3:13 PM
hi Jans,
i need a few sample auto transformer projects,
if you have that can u send me as .pdf
thanks...
05/07/2010 12:22 PM
@Guest
I do not have anything ready made.If you could please furnish specific requirements i will try to prepare a sample scheme and try to forward .Generally auto transformers are huge
+50 mva and as such must be treated in detail to avoid any expensive error.
05/01/2010 5:09 AM
Hai Mr. Jans is absolutly correct.
Further more information see below links.
http://wwhttp://www.gedigitalenergy.com/multilin/notes/artsci/art11.pdf
www.ceerelays.co.uk/brochures/CEE%20PRAG.pdf
Hanu