Difference Between Iu & Ith

05/02/2010 11:15 AM

Can you help me guys know the difference between Ith & Iu rating in MCCB?

I have an MCCB with the rating of Ue = 660 volts & Iu = 1250 Amps

It as a rating also of Ith = 800 amps max @ 45 deg C & Ir = 6300.

I have a motor for my chiller which requires a MCCB with min. ampacity rating of 911 amps. tthe voltage is 380 volts, 3 phase 60 hz. can i use this MCCB with a rating of Iu = 1250 Amps and Ith = 800 A max at 45 degree C.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Difference Between Iu & Ith

05/02/2010 9:01 PM

Noope!

53 2E 4D 2E

Register to Reply Score 1 for Good Answer
Commentator
Australia - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jan 2008
Location: Mount Gambier, South Australia
Posts: 56
#2

Re: Difference Between Iu & Ith

05/03/2010 5:45 AM

Having a Ith = 800A max, whereas you need a min of 911A so it is a little under size.

__________________
tooz
Register to Reply
Anonymous Poster
#3

Re: Difference Between Iu & Ith

05/03/2010 7:39 AM

So far I know ,Ith is the thermal current of circuit breaker in air.For this value circuit breaker will trip.The more circuit breaker current than Ith circuit breaker will trip more faster.On the other hand,Iu is the uninterruptable current.So circuit breaker can carry it without tripping.

In your MCCB ,Iu is higher than Ith.How?

I think you should choose a MCCB ,Iu rating more than 911A.

Thanks

Fakrul

Register to Reply
Associate

Join Date: Nov 2009
Posts: 42
#4
In reply to #3

Re: Difference Between Iu & Ith

05/03/2010 8:39 AM

Yup ur right. That's why I find it strange too. Iu is 1250 A while Ith is 800 A max. That's why i wonder what the use of Iu 1250 amps when @ 800 A it will trip already. Thanks guy for your help.

Anyway the MCCB is made of ABB SACE model SN1250.

Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2009
Location: Ukraine
Posts: 5
#5
In reply to #4

Re: Difference Between Iu & Ith

05/13/2010 8:23 AM

Why wouldn't go to ABB catalogs to verify.

Register to Reply
Anonymous Poster
#6

Re: Difference Between Iu & Ith

06/09/2010 6:03 AM

See page 10

http://www.gil-lec.co.uk/custom/upload/pdfs/circuit%20protection/Hager_Isolators_Switches.pdf

Register to Reply
Register to Reply 6 comments