Short Circuit Connection

05/02/2010 11:30 AM

My customer says that his LV network short circuit (SC) current is 65KA and peak SC is 137 KA. Please tell me how does it affect the motor designer. E.g is my customer expecting 65 KA to flow through the motor windings (stator/rotor) for certian duration e.g 65KA for 0.25 sec.? Please clarify.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Short Circuit Connection

05/02/2010 11:43 PM

Oh no. There is no chance of this 65kA flowing through the motor. This is the fault current which would occur if the system sees a 'bolted short-circuit' at the output of the transformer/s. This figure is required to select appropriate circuit breakers. Your motor will be protected adequately by a proper circuit breaker in the event of any short-circuit, and by a properly sized relay under overload conditions. There is no chance of any short-circuit downstream of the motor is there?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Short Circuit Connection

05/02/2010 11:50 PM

I suppose the circuit breaker will require some time to trip therefore is there a chance of 65KA flowing through the motor for few milliseconds.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #2

Re: Short Circuit Connection

05/03/2010 12:14 AM

No. You see, all electrical connections will come and TERMINATE at the motor terminals. Whatever the mode of starting of the motor, there is no electrical equipment DOWNSTREAM of a motor ... so there is no chance of any fault current flowing through the motor windings.(.. unless there is a short-circuit in the motor windings themselves .. in which case, no point in protecting it )

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2010
Location: India
Posts: 42
#3
In reply to #1

Re: Short Circuit Connection

05/03/2010 12:05 AM

For interesting articles, newsletters every fortnight, visit and register at www.maintenancecircle.com

Maintenance Circle Team(R)

__________________
Writer Anand
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Short Circuit Connection

05/03/2010 1:02 AM

The motor design/selection does not depend much, if at all, on the available short circuit currrent. This number is used instead for selecting fuses and/or circuit breakers that are capable of interrupting such current. (Some typical interrupting ratings are 10kA, 22kA, 100kA, 200kA, and others; which must be selected to equal or exceed the available short circuit current through the device.)

Because of the impedance of conductors from a breaker to a motor, the available short circuit current at the motor will be less than that at the breaker, but still it must be protected against.

Normally, the starting current of a motor is the maximum it will receive (around 6x full load current, depending on specifics). The 65kA (or 137kA) would not typically go to the motor, but rather to a shorted bus bar or cable "upstream" of the motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Participant

Join Date: May 2010
Posts: 4
#6

Re: Short Circuit Connection

05/03/2010 12:39 PM

I am grateful to you all for illustrative explanations and prompt help.

Please also explain what is the difference between 65KA (steady state) and 137 KA (instantaneous). Are there any standard duration for both?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Short Circuit Connection

05/03/2010 3:07 PM

Depending on the point of the voltage wave at which short-circuit occurs, there will be a DC component which makes the current wave offset ... something like this one...a detailed explanation you can get from

http://www.energy.siemens.com/us/pool/us/services/power-transmission-distribution/medium-voltage-product-services/tech-topics-application-notes/techtopics44rev1.pdf

As per IEC, the circuit breaker with a 65kA capacity must clear a fault with a peak of 143kA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); K P Anoop Moosad (1); kvsridhar (3); maintenanceanand (1); Tornado (1)