Re: What is the Difference Between "Metering CT" and "Simple CT"
05/03/2010 12:28 AM
Hi
A metering CT will be of higher accuracy class may be of <0.5% or better typically 0.2% (most common for this purpose).
A general CT can be of >1% accuracy, may be ok for protection circuits or for indication of current in the monitoring panel, not for accurate measurement purposes.
05/03/2010 1:11 PM
very generally saying:
metering cts have better accuracy at rated current and below and saturate quickly and can be set to saturate say at 200%.thus protecting sensitive meters under fault conditions.protection cts generally have comparitively inferior accuracy at rated current but can be set to reproduce currents as high as 20-50 times or even more with about 5-10% accuracy.
metering ct function is important when there is no fault but protection ct performance is important under fault conditions.