NFPA 70E

05/06/2010 9:46 AM

I have a generator room and was wanting to set the Instantenous portion very high or not at all to coordinate better with my downstream devices and the alternative to that is very high arcflash. So here is my thought I tie the door contacts and motion sensor for the room into the instantenous portion of the circuit breakers. My thought is while nobody is in the room then arc flash is irrelevant.

My concern is while somebody's in the room and the generators aren't on therefore the instaneous portion is on and the generators fire up I just have to coordinate any inrush with my temporary instaneous.

Any other concerns?

__________________
guest
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#1

Re: NFPA 70E

05/06/2010 3:05 PM

fit lockout device to door so before entry padlocks have to be fitted to keep door open and disable system.

as a back up movement sensors could be used in case operators bypass lock out then anyone moving in the room will be detected

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#2

Re: NFPA 70E

05/07/2010 11:12 PM

Thanksinadvance,

Welcome to the site. I wonder if your facility can afford the risk I see in your suggestion. At the same time, I understand your desire to minimize "nuisance" trips. Interconnecting the settings and the supposed presence or absence of personnel doesn't seem to be wise, in my thinking. Over time, the reasons for the interconnection can be forgotten or be viewed as unimportant or be seen as a nuisance. The settings you use should be for safety to the equipment and processes the equipment serves. Arc flashes represent the energy released in a fault condition, not the "cost of doing business". I feel that you would want breaker settings that are protecting the equipment---all the time.

JMM

Register to Reply