Conveyor Zero Speed Switch

05/06/2010 9:37 AM

In conveyor system using ZSS in tail pulley for detecting low spped when low spped occurs(problem in belt, belt cut) it sence the low signal and gives to PLC, PLC trip the conveyor. We using KANA ZSS relay sensor.

I want to know a proper interlock in PLC by logic. Presently no interlock in our system. In running condition conveyor trips in ZSS after electrical and mech clearnace started again.

Plz give the idea for improving ZSS interlock in conveyor systems.

__________________
Arun Babu
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: Conveyor Zero Speed Switch

05/06/2010 11:07 AM

encoders connected to drive roller and take up roller. Counts from both can be used to sense those failures, also slippage under load for belt tensioning and belt over load.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Conveyor Zero Speed Switch

05/06/2010 1:46 PM

In the PLC logic you could incorporate a timer that bypasses the ZSS, giving time for the conveyor to come up to speed (maybe 10 seconds or so).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#4
In reply to #2

Re: Conveyor Zero Speed Switch

05/07/2010 10:18 PM

Yep. Since the PLC is evaluating its logic at a much faster time rate than the starter can energize the motor and get its driven load up towards speed, a time delay in the program is the correct solution. Write it so the switch input is ignored for a brief time after the starter is energized. The suggested ten seconds is much longer than you need--try 2 or 3 seconds instead. Don't program it as a delay on response to a zero speed input. In other words, the input condition for the timer is the motor starter being energized, not the signal from the zero speed switch.

--JMM

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#3

Re: Conveyor Zero Speed Switch

05/06/2010 10:50 PM

Could you tell us more about the application?

minimum speed in rpm of the drive

a very basic & easy method is to install a tab or flag of metal on the driven shaft, use a proximity switch to send a signal to the plc

a couple of logic [software] timers

one to determine the shaft is above minimum speed

one to bypass for start up

I couldn't find any info on the relay you mentioned

I would guess it provides a simple output for either a moter starter or plc

Register to Reply Score 1 for Good Answer