Line Current in a 2 wm Test

05/06/2010 8:45 AM

If I have a balanced load and 1 meter leads +35kW and the other -29kW how can I calculate the load power factor and the line current if the line voltage is 630V.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Line current in a 2 wm test

05/06/2010 8:52 AM

Is the negative 29kW load a power source?

Reply
Anonymous Poster
#2
In reply to #1

Re: Line current in a 2 wm test

05/06/2010 8:57 AM

sorry that should be negative 20K.

I'm trying to figure out some examples in a text book.

What I can't figure out is how I can get the the appartnt power with out knowing the line current. Can I calculate the line current from the voltage and the P1, P2.

There is no mention of the load being a soarce.

Reply
Anonymous Poster
#3
In reply to #1

Re: Line current in a 2 wm test

05/06/2010 8:59 AM

I guess the example is talking about a motor as a load so not a soarce, right?

Reply
Anonymous Poster
#4

Re: Line Current in a 2 wm Test

05/06/2010 9:10 AM

The first examples I did provided me with a value for the three lines and a voltage. This is not problem, I calculated the apparent power then the active and got from that the Pf.

The active power in this example will be 35-20=15kv.

Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#5

Re: Line Current in a 2 wm Test

05/06/2010 9:28 AM

You can calculate power factor by dividing true power by apparent power.

Reply
Anonymous Poster
#6

Re: Line Current in a 2 wm Test

05/06/2010 9:42 AM

True, but how could I get the apparent power without being provided a line current? In previous examples I have done, I was told the line current, therefore I calculated the apparent power and then divided that by the active power to get the pf but how can I get to the same place when not provided with the line current?

Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Line Current in a 2 wm Test

05/07/2010 1:52 AM

In Three phase electrical circuit power can be calculated with the help of following relationship

Cos ф = Tan-1 √3*(W1-W2)/(W1+W2)

For power factors less than 0.5, one of the wattmeters would read negative.

Reply