Current Output From a 3-Phase UPS

05/07/2010 1:56 AM

Please I need to confirm that the current output from a 3-phase UPS remains the same, when being powered by the grid and when in UPS mode.

A client of mine has argued that the current output from a 120kVA UPS (400V phase -phase) will be about 57A per phase when on battery mode.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: CURRENT OUTPUT FROM A 3-PHASE UPS

05/07/2010 2:15 AM

120,000VA ÷ (400V x √3) ≈ 173 A. How is the 57A being derived?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2009
Posts: 6
#2
In reply to #1

Re: CURRENT OUTPUT FROM A 3-PHASE UPS

05/07/2010 3:22 AM

He divided the current by 3. that is 173A/3 = 57A.

He reckoned that when the UPS is supplying the load via the batteries the current per phase will be 57A.

I am sure this cannot be correct.

but I just need confirmation that it is not.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: CURRENT OUTPUT FROM A 3-PHASE UPS

05/07/2010 3:37 AM

The division by √3 already makes the proper correction for each single phase. Dividing by 3 again is completely incorrect. But it's sometimes tough to deal with pointy-haired bosses/clients. All join in now for the Dilbert theme song!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#4
In reply to #3

Re: CURRENT OUTPUT FROM A 3-PHASE UPS

05/07/2010 7:49 AM

Yeah me too agree to tornado.

Register to Reply
Member

Join Date: Apr 2009
Posts: 6
#5

Re: Current Output From a 3-Phase UPS

05/07/2010 9:12 AM

Thank you very much.

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #5

Re: Current Output From a 3-Phase UPS

05/07/2010 10:38 AM

The UPS output current totally depends on the load, not on the UPS rating. The rated current of the UPS determines the maximum current that UPS can supply. It is absolutely true that the current of UPS output remains same if the UPS output voltage and the load are same, regardless of the power supplied from utility or from the battery bank. In some circumstances, the UPS load may change if the utility supply fails (example: for the plant safety shutdown system, the UPS load increases when the AC power is lost due to the activation of safety shutdown system) and the UPS current may also change when the UPS is powered by the battery bank. So, discuss with your client and find the correct reason why he/she feels the UPS load is 57A when it is on the battery.

The maximum current/phase of a 3 phase, 120 KVA UPS is 173 A, not 57A – it is for sure.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#7

Re: Current Output From a 3-Phase UPS

05/07/2010 11:11 AM

Amp hour tells the capacity of battery. So 57 amps for more time but if load draws current maximum it can supply is 171 for proportional less time.

Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".