Capacitor Bank

05/08/2010 2:19 PM

sir kindly can u tell me how to find out the Kvar rating if the load is given (KW)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Capacitor Bank

05/09/2010 1:24 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#2

Re: Capacitor Bank

05/10/2010 5:12 AM

1800KW

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Capacitor Bank

05/12/2010 10:44 AM

Capacitor kVAR Required = kW (tan phi 1 - tan phi 2)

where kW is the connected load

phi 1 is the power factor angle of existing power factor [cos -1 (pf1)]

phi 2 is the power factor angle of target power factor {cos -1 (pf 2)]

Reply