Minimum Distance Between Two Conduits?

05/10/2010 7:04 AM

what will be the minimum distance between two conduits?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Minimum Distance Between Two Conduits?

05/10/2010 9:00 AM

As always, the correct answer to this type of question depends upon the code rules, if any, in effect where you are doing this work. As such, you have not provided enough data for any meaningful answer.

Having said that, if this work was being done in Canada, there is no "minimum distance" required between conduits.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Minimum Distance Between Two Conduits?

05/10/2010 11:18 AM

Generally, the minimum distance (in the US) ends up being based upon whatever mounting/bracing system you are using. The mounting system will vary by application, i.e. Seismic Bracing, passing through fire walls etc. etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#3

Re: Minimum Distance Between Two Conduits?

05/11/2010 3:46 AM

This will depend on where you install the conduits , type of conduit , and what voltage used in the service...in concrete?..embed in wall?...or open surface conduting......PVC conduit or GI conduit?...wires inside the both conduits are same voltage or not?...what is the supporting system used?...saddles?...clamps?....If you find the answer for these , you will get the answer for your question.

Register to Reply
Anonymous Poster
#4

Re: Minimum Distance Between Two Conduits?

05/11/2010 8:08 AM

There is no such requirements of min. distance between conduits, as long as they are operating at the same voltage (i.e., 230 V).

Only if a conduit is carrying IT/LAN cables, then the min distance btween, IT/LAN and electrical shall be 300mm

Regards,

PG

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Minimum Distance Between Two Conduits?

05/11/2010 12:00 PM

If they are in contact with each other, the distance will be zero.

Can the answer be found in British Standard 7671?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2009
Posts: 47
#6

Re: Minimum Distance Between Two Conduits?

05/13/2010 3:46 AM

Conduits for what? this is layed in side the concrete or open buried or trench,GI or pvc please specify