If there is a mesh with 64 earthing rods, should the rods for transformer neutral grounding be separate or attached with the mesh?
Re: Neutral Grounding Question
05/10/2010 11:06 PM
The purpose of netural and general is different....Transformer neutral is grounded because your transformer
will be the impotant electrical equipment and this has to
be protected for fault i cannot have a neutral floating and
it has to be earthed properly. It is also earthed in order
to reduce the 3rd Harmonics effect.
I hope its now very clear to you.
05/11/2010 4:13 AM
Neutral earthing is for getting proper potential difference in Y connection. It is recommended to have seperate earthing for Neutral.
05/11/2010 8:05 AM
First of all let me congratulate you for asking a very good question.
As per TNEB (tamil nadu electricity board, india) rules, the neutral is also a part of the total earth grid.
The same applies to UPS neutral
Regards,
PG
Good Answers: 170
05/12/2010 10:18 AM
No need to have any doubt. You MUST connect the transformer neutral earth rods also to the substation earth mat to create an equi-potential plane.
05/13/2010 3:39 AM
the over all earth value is below 2 ohms its ok for transformer neutral grounding also