How is the Conversion factor (V/f) used in VFD?

05/12/2010 4:55 AM

I have been reading information on VVVF (VFD) and came across this Conversion factor (V/F). How is it used in frequecny or voltage variation in the VVVF (VFD)?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Associate

Join Date: May 2009
Posts: 40
Good Answers: 1
#1

Re: How is the Conversion factor (V/f) used in VFD?

05/12/2010 5:09 AM

In the VFD drives the ratio of V/f remains constant.so by changing frequency you can set the voltage flucations..........

Hope this would helps.........

Reply
2
Anonymous Poster
#2

Re: How is the Conversion factor (V/f) used in VFD?

05/12/2010 7:55 AM

The magnetic flux (or the density) remains constant if V/f is maintained constant.

(faraday's law)

V = ndΦ/dt

= n (ω=2πf) ΦmaxCos ωt

If the Φmax is constant,

V1/V2 = f1/f2

or

V1/f1 = v2/f2 = constant

Or if you want it simpler,

Vrms = √2πNfΦmax = 4.44 NfΦmax

Φmaxis the maximum ie peak value of the flux - which must be held constant in view of the magnetic circuit of the equipment.

So

Vrms/f = 4.44 NΦmax = constant.

Reply Good Answer (Score 2)
Anonymous Poster
#3
In reply to #2

Re: How is the Conversion factor (V/f) used in VFD?

05/12/2010 5:23 PM

Excuse my ignorance- what is VFD?

What that system is used for ?

Reply
Anonymous Poster
#4
In reply to #3

Re: How is the Conversion factor (V/f) used in VFD?

05/12/2010 10:40 PM

VFD = Variable Frequency Drive.

This is usually used (and very frequently nowadays) for controlling the motor speed.

It has also (hence) the capability to start the motors.

It does its activity by changing the line frequency of the AC current.

Reply
Anonymous Poster
#5
In reply to #4

Re: How is the Conversion factor (V/f) used in VFD?

05/13/2010 4:50 AM

Yes,that is used in the new laundry washing machines.

Do you have some idea about circuit theory of that drive ( circuit board) ?

Reply
Participant

Join Date: May 2010
Posts: 4
#6
In reply to #2

Re: How is the Conversion factor (V/f) used in VFD?

05/22/2010 2:40 AM

Thanks, I appreciate this response.

Furthermore, if (V/f) changes and causes a change in magnetic flux, will that affect the current within the motor?

Reply
Anonymous Poster
#7
In reply to #6

Re: How is the Conversion factor (V/f) used in VFD?

05/22/2010 4:10 AM

Almost in all cases yes. however the VFD will ensure that you do not cross the limit.

It is like this.

The power

P = VICosΦ or √3VI CosΦ (3 phase)

The speed of the motor (as controlled by VFD will be at the the slip speed) and hence we will not consider the other high slip phenomenon.

At different speeds, obviously the load will demand different power.

if it is a resistive load - the power of course will be linear with voltage

If it is pump then you have to look at the pump characteristics, and its power requirement at different RPMs (Operating characteristics as I mentioned earlier).

Similarly any load will have its own typical OCC (operating characteristics curve)

In normal motor what we do overlap the load OCC with motor curve. The intersection of OCC with motor curve will provide the operating point (slip and thus RPM, power, power factor, ...)

here we will neglect the slip for simplification (or in fact will go for the slip at the maximum power condition) and then calculate the load for each RPM (Watts, KWs) and then go back and based on motor efficiency calculate the current for each RPM (and from there based on slip to frequency)

This will provide you approximately the I-f characteristics for the motor-load combination.

However there is a good possibility that the current for a particular load- a few not very common loads are there, (but that is only if the system is improperly designed) will cross the rated current. Any good VFD if married well to the system will trip/ control the current in these condition, and in either cases most likely the motor will stall.

Secondly you must remember that the current carrying capacity of the conductors (stator) are much higher at low frequencies - lower skin effect.

And manipulating all these, and also a few other factors, the VFD drives are able to provide 1.5 times or even more torque at lower frequencies (this characteristics of having very high starting torque in AC Motor is not available in any other starting mechanism)

Reply Score 1 for Good Answer
Participant

Join Date: May 2010
Posts: 4
#8
In reply to #7

Re: How is the Conversion factor (V/f) used in VFD?

05/22/2010 4:51 PM

Thank you once again.

This is absolutely clear to me.

Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); ieshiv (1); Snakey (2)