One of the our Raw mill motor (cement mill) Motor differential Relay is tripping
Motor kw 4800
volt 6600v
A 470
Freq 50HZ
RPM 992
PF 0.81
Motor CT ratio 500/1, class-ps,Vk-79.3v
Panel CT ratio 500/1, class-ps,Vk-79.3
Protection relay type ABB REM-545
During the no load run test, the set value 5% Differential (recommended)
During the load test, the motor get tripped in differential protection. The recorded data is 11% of differential current (load current was 270A with capacitive load)
And again we started the motor with Diff setting of 30% . During load condition, the motor achieved 80% of the full load current at that time the diff current sensing is (11-12%)
Note:
1.The relay stability is tested with 3φ sec injection kit and it is found ok
2. Stability is tested by current method between the motor CT & pnl CT and it is found ok
3.CT polarity and its sec connections are ok
4.The CT ratio's are 500/1 as mentioned above
5. CT star points are done as per the diff scheme and grounded at both ends
6.The cable internal CT wiring is 3c×2.5sqmm cu multistand and cable from the motor CT is is 3c×2.5sqmm cu single stand(length 130mts)
Please help us what is the reason for the tripping due differential current protection
with regards
jcg154