Anonymous Poster

Seal Pot for Gas Service

05/17/2010 5:05 AM

seal pot has been used for gas service to install the DP flow measurement transmitters in order to locate them below tapping point...

does it require filling liquids in impulse tube?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#1

Re: Seal Pot for Gas Service

05/17/2010 9:53 PM

Note the installation practices for gas versus steam in the graphic below:

These installation techniques are done to

- prevent liquid condensation from collecting in the impulse tubing and creating measurement errors on a gas pipe.

- prevent steam from cooking/baking/overheating the pressure transmitter by isolating the transmitter from the steam with condensed water, which acts as a pressure transmission medium

- keep gas/air out of a liquid impulse sensing line by allowing any gas/air to rise back up to the flow line.

A seal pot or condensate pot is installed in the impulse tubing on a steam line. It is filled with water to isolate the transmitter.

Could the line be a former steam line, now used for water? The seal pot could be left over from steam service.

Reply
Anonymous Poster
#3
In reply to #1

Re: Seal Pot for Gas Service

05/18/2010 10:22 AM

Thaks carl...

U r correct this is the normal installation technique for liquid/gas/steam services.

but here in this case if transmitter installed above tapping point for Gas service it is not accessible (no platform for access).that's why it has been advised to use seal pot and install the Tx below the tapping point...

do we need any filling liquid for this case?

will this kind of installation will provide any error on measurement?

Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#2

Re: Seal Pot for Gas Service

05/18/2010 10:13 AM

To clear things up, the pots are referred to as condensate pots if they are used in gas service where the transmitter is mounted below the tapping not seal pots.

In this case the purpose of the pots is to collect the condensate which will inevitably form thereby preventing the accumulation of condensate in the impulse lines, the impulse lines must be kept free of condensate in order to prevent erroneous measurements since it is impossible that both impulse lines will fill at the same rate. There is no requirement for impulse lines in this type application to be liquid filled.

Seal post are used for steam flow applications in which case the transmitter should be mounted below the tapping and the impulse lines and the seal pot must be filled so as to protect the sensor from exposure to high temperature steam. Also it is inevitable that the impulse lines will fill with liquid since steam will condense once it exits the flow stream.

Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#4

Re: Seal Pot for Gas Service

05/19/2010 10:28 AM

It is not uncommon to use a drip leg as a place to allow condensate to collect:

Reply