Thermocouple Testing

05/17/2010 5:02 AM

how to test the thermocouple (Type K) to confirm it's working or not?

what is the test equipment?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#1

Re: Thermocouple Testing

05/17/2010 9:37 AM

An other temperature sensor in parallel and compare results.

Reply
Commentator

Join Date: Dec 2007
Location: texas
Posts: 92
Good Answers: 8
#2

Re: Thermocouple Testing

05/17/2010 8:45 PM

Hi,

A simple way of testing a thermocouple to confirm if it's "working" assuming that it is in a thermowell and can be pulled out of it.

1) Disconnect the wires going to DCS or PLC located in the thermocouple's weather head

2) Find out what's the ambient temperature at that location

3) Put the two wires going to DCS or PLC together and see if the temperature reading on DCS or PLC matches the ambient temperature,if it does then the loop is working OK

4) Pull the thermocouple and reconnect the wires.Hold the thermocouple in the air for a few minutes if the reading on DCS or PLC matches the ambient temperature the the thermocouple is OK.

It's a lot easier to test the thermocouple with testing equipment please let us know what equipment you have access to and I will try to help you.

Thank you

__________________
"The older I get -The better I was"
Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#3

Re: Thermocouple Testing

05/18/2010 1:47 AM

Firstly, Using an ohm-meter check the resistance across both leads it should be 0 ohms.

Secondly, disconnect the TE from the transmitter or extension cable terminal assembly and use the appropriate test equipment (thermocouple calibrator or millivolt-meter) measure the actual temperature, if you have persons who are familiar with the process they will be able to tell if the readings are realistic. Note that this is not a conclusive test.

Or

Thirdly (this is the best way of testing), if the TE can be removed from service use a calibrated/certified temperature bath and temperature calibrator to verify the operation of the TE.

Reply
Member

Join Date: May 2010
Posts: 6
#4

Re: Thermocouple Testing

05/29/2010 12:11 PM

hello you can simply unwire the connection on the TC it self and measure the MV reading with multimeter and compare with this table http://srdata.nist.gov/its90/download/type_k.tab

Reply
Commentator

Join Date: Aug 2011
Posts: 76
#5

Re: Thermocouple Testing

08/22/2011 5:37 AM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply Off Topic (Score 5)
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

dabdool (1); electricaleng (1); mahraan (1); nick name (1); wrenchpuller (1)

Previous in Forum: Use of 2 SOVs in S/D valves   Next in Forum: Seal Pot for Gas Service

Advertisement