What is the (V/f) Factor in VFD (VVVF)?

05/19/2010 2:52 AM

I have been reading through information on VFD/VVVF and came across this factor (V/f). How is the "voltage or frequncy" varied using this factor to actually vary the speed (RPM) of the VFD driven motors?

Register to Reply
Pathfinder Tags: VFD
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: What is the (V/f) factor in VFD (VVVF)?

05/19/2010 7:43 AM

Did you post this?

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2

Re: What is the (V/f) Factor in VFD (VVVF)?

05/19/2010 9:02 PM

Synchronise speed =120f/p so if you vary the frequency speed is varied torque is proportional to square of voltage so we get a good torque variation also. Thyristor firing is done to get variable output.

Register to Reply
Participant
India - Member - Engineer Indonesia - Member - Engineer

Join Date: Mar 2010
Posts: 3
#3

Re: What is the (V/f) Factor in VFD (VVVF)?

05/19/2010 11:54 PM

V/F factor is the ratio to keep constant torque at higer speed to lower speed. In VVFD, Voltage is varied with frequency keeping this ratio constant so the MOTOR operates with contant torque. In physics formula, Power(P) is directly proportional to Torque(T) X Speed(N) i.e. (F). So to keep constant torque

T α P/F so T α (V / F) * I ( Where I is depend on mech. load)

So in VVVF drive, by keeping V/F ratio constant varying it is able to get constant torque or variable torque at low speed which is not possible in case of constant speed( i.e. without VFD)

Register to Reply
Participant

Join Date: May 2010
Posts: 4
#4
In reply to #3

Re: What is the (V/f) Factor in VFD (VVVF)?

05/20/2010 1:15 AM

Thanks gentlemen, I think you both have provided me fair explanations.

Thank you so much.

Register to Reply
Anonymous Poster
#6
In reply to #4

Re: What is the (V/f) Factor in VFD (VVVF)?

05/21/2010 9:07 AM

The guest is correct. Please look at the link given by me on #1

P = Tω correct

So

T = P/ω = k. P/f correct

ο V/f wrong

since I is not dependent on mechanical load VI cos Φ or power is what demanded by the load and not current.

conversion of mechanical parameters into electrical parameters is not so simple since the P itself is dependent on ω (check any load's operating characteristics)

The other guest (I don't know why he has marked himself OT) has pointed out, it is the magnetic flux density.

read the explanation given in the link of #1.

Register to Reply
Anonymous Poster
#5

Re: What is the (V/f) Factor in VFD (VVVF)?

05/20/2010 4:03 AM

hi friend, i wont agree with u people

V/F factor represents the Flux value

if we increse the voltage by keeping frequency constant, flux will increase this will saturate the core and wdg.

this will effect the motor performance ....

Register to Reply Off Topic (Score 5)
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); hithuanand (1); rajen.jethva (1); Snakey (1)