Electrical Engineering Spec Gone Bad.

05/19/2010 4:37 AM

Advice and comments please.

We are wrapping up a project where we supplied 2 x 112kw soft starts. The only information on any of the tender documents with reference to sizing the units was 112kw. As it turns out the motor is a 150hp, its name plate fla is 190, we measured it and it shows a draw of 209a. They are saying the soft starts are under sized, which they are, but we supplied what we were asked according to the information given. They are saying that if we didn't know the amperage of the motor we should have asked. My thoughts are how did they derive the 112kw rating.

This is the first time I have ever ran into this with any Eng / consultant co. we submitted our approval drawings for their review and they came back as approved. We are never given the mechanical data, we always quote from the electrical specifications.

I do know what happened, the electrical engineer that started the project left as it was being tendered, the one that is still there has been an office manager for 30yrs, my opinion he stamped them without looking at the approvals.

The lead engineer is a civil engineer who has stated to me on the phone that " it is not our responsibility to approve or verify, we merley glance over the approvals to make sure the general scope of the spec is met". I know this seems like bull,, but I wrote it down after he said it, I almost fell out of my chair.

Side note, the gen set was also undersized on this project, they obviously never covered the approvals on that either.

How do I argue this and keep the end user, the general contractor and the electrical contractor happy at the same time without alienating the engineer. The general and electrical contractor all know and side with me, but they are not getting paid as there is obviously issues with this projects completion.

The engineer doesn't care as long as someone else takes responsibility for something in my opinion he has missed. On the phone with me he is placing blame with the general and electrical contractor, on site when I was not there he is trying to tag me with the issue.

please send me your thoughts.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Electrical Engineering spec gone bad.

05/19/2010 5:47 AM

Usually the consultant along with the client does the inspection of any material (panel/DG set/transformer) etc at the vendor's factory. Once he is assured that the material is in line with the specs. he gives a dispatch clearance, in order to dispatch the material to site.

Has the dispatch clearance been obtained, in this case, from the consultant? Even, if the answer is no, you can still sue the consultant. I hope, consultant has given in writing, his approval for manufacturing of soft starters.

Regards,

PG

Reply
Anonymous Poster
#3
In reply to #1

Re: Electrical Engineering spec gone bad.

05/19/2010 9:21 AM

Stamped approvals have been given, order to proceed.

Reply
Anonymous Poster
#2

Re: Electrical Engineering spec gone bad.

05/19/2010 7:05 AM

What is the operating voltage?

112KW = 150HP.

The FLA @0.8pf, 415V is 194A and 0.8pf, 380V is 212A.

What is the motor name plate voltage ?

Is it that you are trying to control at different voltage? Why should load draw larger current than FLA

The question is not how they derived the 112KW rating, rather there will be a rapid degradation of the motor if this FLA is maintained for a long time. What has gone wrong ? After all the current is 10% more than the rated.

Reply
Anonymous Poster
#4
In reply to #2

Re: Electrical Engineering spec gone bad.

05/19/2010 9:30 AM

600v is the system voltage. The pump manufacture I believe is running the motor in the service factor, or exceeding it.

Reply
Anonymous Poster
#9
In reply to #4

Re: Electrical Engineering spec gone bad.

05/20/2010 8:21 AM

P = √3VI CosΦ

112000 = √3 x 600 x I x 0.8 (assumed)

I = 134.75 A/η

Note I am talking about FLA and not the starting current on DOL.

@209A it is 174.η KW and even at name plate 190A it is 157.η KW electrical inputs

Now even if I take efficiencies of 0.9 (quite poor) it is

150A, (and 156KW / 141 KW other two cases)

Are you working with single phase motor at this voltage/power?

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#13
In reply to #2

Re: Electrical Engineering spec gone bad.

05/23/2010 12:01 AM

stndard motor should be suitable for +-6% .in India now all motors are made for +-10%.He should have ctered for 415-10% while designing the starter.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
2
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#5

Re: Electrical Engineering Spec Gone Bad.

05/19/2010 10:36 AM

The spec did not go bad. The specifier and the person who approved and stamped the submittal have gone bad.

You must argue that you supplied what was required based on the specification and the approved submittals.

The fact that you have stamped approvals, that is the end of the story….period!

The person that stamped the approvals is the responsible party….period!

I am going on the assumption that you were not aware of any irregularity between the motor and the soft start units based on the contract documents prior to the approval, release and order of the soft start units.

When presenting your case to the owner and/or GC keep your comments limited to "we provided what was spec'd. Our submittal was approved. We supplied the approved submittal to the manufacturer. We furnished and installed the equipment based on the approved submittal". Offer nothing additional.

The A/E will never admit fault but you must stick to your guns on this. Remember, the A/E are the specifier, not you the contractor.

Having been involved in many, many disputes of this nature the only advice I can give is do not allow yourself to get bullied or intimidated into this p*ssing match.

Check back and let us know how this worked out.

Good luck sir!

__________________
The first 5 days after a weekend are always the hardest................................
Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#6

Re: Electrical Engineering Spec Gone Bad.

05/19/2010 10:54 AM

You're into the awkward realm where business and engineering clash. The key factor your company's upper management need to decide first is the value of this customer to your company. Now depending on how valuable this customer is to your company one of these scenarios will be decided by management:

  • All efforts to rectify this design short coming will be paid by your company to keep this customer happy. Chalk up these losses as part of the learning experience in dealing with this golden client.
  • Design up a more robust system that will handle the actual loading this customer has instead of the claimed loading. Offer this new system at a reduced price (possibly a loss for the upgrade) to the customer.
  • Hand over the dispute to the lawyers. Be prepared to demonstrate that your existing design meets the specifications.
__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Electrical Engineering Spec Gone Bad.

05/19/2010 2:38 PM

600V, you must be in Canada.

Here in the US, nearly every bid specification I have ever worked on had a CYA clause buried in it somewhere telling any bidder that THEY are responsible for verifying equipment sizing and ratings etc. That responsibility, often referred to as something like "vendor coordination", is usually assigned to a General contractor, if there is one, because THEY are the one's who will see both the mechanical specs and the electrical specs. it is probably buried in the general specifications and/or qualifications of bidders sections in Division 0100 or thereabouts.

There is no way a consulting engineer can know, in advance, what a motor's nameplate FLA is going to be. He can specify a MINIMUM power rating, but how a vendor meets the performance criteria is up to them. Sorry to break it to you, but you made a classic rookie error. I was in the soft starter business for 30+ years, one thing I always taught my people was "HP means nothing, current means everything". In other words, I think you should have known better. When I bid projects with potentially nebulous specs, I would always make my bid crystal clear, i.e. "This equipment is proposed to meet specification section XXX.XX.X as stated in the bid documents, but the maximum current rating of the soft starter will be 180A (or whatever yours was). Any deviation from these values will be the responsibility of the purchaser." Now mind you, I had a lot of people refuse to accept that and insisted that I bid a larger unit, but I did it to make sure I was not going to lose the job to a rookie, like you, who was not properly addressing the issue

Bottom line, I personally think you or the contractor you sold it to need to suck it up and provide the proper device. The CE is correct. Even though he signed the drawings, he did not absolve anyone of the basic responsibility of coordinating specifications between vendors.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Power-User

Join Date: Sep 2009
Location: N38º3', W085º3'
Posts: 326
Good Answers: 19
#8

Re: Electrical Engineering Spec Gone Bad.

05/20/2010 8:09 AM

When I was on the construction side of the fence, I tried never to present a problem that would discredit the engineer or architect I was working with. Instead present them with a "better" solution to what they all ready (maybe) new.

They don't want contractors to fail and will generally work with you if you don't immediately put them on the defensive. We have stock forms that contain language I hope I never have to use.

The request involves a patent ambiguity or conflict in the documents that should have been addressed during bidding. Provide the better quality or greater quantity work, in accordance with Supplemental General Conditions.

It would have been a good idea to bring this up during the bidding phase. An addendum could then have been written to address the problem and keep the bidders on the same page.

__________________
There's a theory stating if anybody discovers exactly what the Universe is for & why it is here, it will instantly disappear & be replaced by something even more bizarre & inexplicable. There's another theory stating this has already happened.D Adams
Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#10

Re: Electrical Engineering Spec Gone Bad.

05/20/2010 10:26 AM

A project manager would also of an engineering background for this.

This is a situation that does occur. One of the thing at time the customer may not have it in there budget at the time to spec. when caught it should be pointed out. There is to blame on both parties, But the customers should pay for the up grade, and the cost of restock charges if it can be returned be shared.

Unless it is the contract requirements from the customer, then it is the customs responsibility, and if they had a consultant, they should turn it over to them for compensation.

It comes down to not pointing fingers (but in essense it is), but accountability.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Electrical Engineering Spec Gone Bad.

05/21/2010 7:17 AM

Dear Guest,

This matter I wanted to reply in the morning but there was some problem in the net.

1.ABOUT INSTALLATION:

The MOTOR H.P. is 150, Full Load current asper Name Plate is 190 Amps but actual is 209 Amps. Starter is SOFT STARTER but details are not furnished in your note. You have not mentioned the speed of the motor. If the speed is 2900 rpm, Power Factor will be bettter and for 750 rpm the power factor will be poor, for 600 rpm, the Power Factor will be still poorer.

Two alternators of 112 kW which means 149.33 H.P each.

2. MY OBSERVATION and RECOMMENDATIONS.:

1. Full Load current Level is alright. If the Power factor is 0.8, the full load current will be 203.66 Amps, but the name plate current is 190 A, and motor manufacturer might have have considered a Power Factor of 0.85 which is also correct.

2. You cannot start a 150 H.P Motor with one Generator of 112kW (150 H.P.), even with Soft Starter. To start this motor, YOU HAVE TO START BOTH GENERATORS and SYNCHRONISE IT and THEN START THE MOTOR.

It is NOT CLEAR from your text whether you have started 2 generators and synchronised to sart the motor. If not tried please try and you may succeed in starting the motor.

3.The selection and sizing of the equipment there is a confusion or bungling and as a man on the spot you have to handle the matter and you are responsible - which is understandable. This is a case of high order irresponsibility by your predecessors.

4. There are lot of discussions in this forum on the capacity needed for a generator to start a motor. Please search in this CR4 links and you will have lot of deails and you can DEFINITELY SOLVE YOUR PROBLEM.

5. MAINLY THE CONSULTANT and the PLANT IN-CHARGE , whether he is CIVIL, OR MECHANICAL, OR ELECTRICAL or ordinary Graduate IS RESPONSIBE, for all these activities in selection of the equipments and CANNOT SHIRK AWAY FROM THE RESPONSIBILITY. If Office Manager has simply stamped and APPROVED he should not be spared and taken to task.

6. I am very eager to know the out come of the issue and i request you to start both generators and synchronise and then start the motor. Please check-up the Droop Character of both Generators for Voltage and Droop Character of the Governor of te Diesel Engine of the Generator for Speed Character. This is very essential. If it does not match, then LOAD-SHARING by the GENERATORS WILL BE A PROBLEM which may be further head-ache.

Please inform the out-come of the issue.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#12

Re: Electrical Engineering Spec Gone Bad.

05/22/2010 11:59 PM

This situation does occur in India quite frequently.Most consultants will qualify their approval with a statement that approval does not relieve the contractor or supplier from carrying out what is required to ensure proper completion and functioning.Now coming to the issue if 112 kw is only is in document.The standard motors should work at 415V+- 6% .When -6% is applied it becomes 390 approx.with this if u calculate the current it may well exceed the 212A.This should have been considered while designing the starter.Motor full load eff and Pf are also to be known.If it is not clear these parameters should have been asked or you should have qualified your offer with a protective clause.However in your drawings and data sheets if u have clearly mentioned the parameters and what current starter can handle and by approving it he has accepted it and you need not worry. by the way have u received the payment.?

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".