What is the difference between clean earth and dirty earth?
All great Ideas are simple
Good Answers: 101
Re: Plant earth system
05/22/2010 6:52 AM
Clean earth isn't dirty, while dirty earth isn't clean.
05/26/2010 10:38 AM
The point of connection to the earth network is the only difference.
Re: Plant Earth System
12/31/2015 2:54 AM
Clean earth is normally for instrument earthing which typically having the measured impedance of ideally 1 ohm (can we really get it?). Dirty earth is normally for electrical which deals with high voltage (and current). The irony is both connections will ultimately go to the same earth that we all live on.