Pressure Compensation for Secondary (Combustion) Air Flow in Boiler

05/22/2010 4:58 AM

Is pressure compensation is required for mass flow measurement of secondary air in boiler?

The primary element is McOn Air (Promecon) sensor. McOn Air measures velocity of air in the duct. Thermocouples are available in the section for temperature compensation.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Pressure compensation for secondary(combustion) air flow in boiler.

05/22/2010 9:24 AM

Yes, pressure compensation is required for accurate mass flow measurement with your primary element according to the manufacturer.

http://promecon.us/Brochures/Air.pdf

Read the paragraph in the lower left corner of the brochure.

Some technologies (ie, thermal dispersion) can be used to measure mass flow without pressure compensation.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#2
In reply to #1

Re: Pressure compensation for secondary(combustion) air flow in boiler.

05/23/2010 1:17 AM

Ace you an ace

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Associate

Join Date: Jan 2007
Posts: 35
Good Answers: 1
#3

Re: Pressure Compensation for Secondary (Combustion) Air Flow in Boiler

05/27/2010 7:45 AM

The pressure compensation for secondary air flow is not much critical as the correction factor density variation is very small. The normal secondary air pressure may be arround 400mm of wcl. The variation in pressure may be + or _ 50mm. Hence the correction factor is 10450/10400 or 10350/10400 respectively that is 1,0048 or 0.9952. This is very negligible. However correction is required for change of temperature for accurate flow measurement.

R.Thiyagarajan

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: Pressure Compensation for Secondary (Combustion) Air Flow in Boiler

11/10/2010 12:23 PM

Abuse/Attack:

This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (1); ducon (1); rajant_2001 (1)

Previous in Forum: Plant Earth System   Next in Forum: The Precise Meaning of Precision

Advertisement