Anonymous Poster

Dry Nitrogen for Transformer Preservation

05/22/2010 11:28 AM

I have a 150MVA transformer that is been preserved with dry air at 0.3kg/cm2. I was told that if the transformer is not leaking the pressure will only vary according to ambient temperature. Right now the dry air in the cylinder is finished and I have refilled the bottle. It is obvious the transformer is not leaking but I am just wondering why the dry air got finished in the bottle. If it is meant to pressurize the transformer inside then why did it get finished?

Thank you for your response as always.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: May 2009
Location: West Point, Texas population around 200.Located between Austin and Houston
Posts: 69
Good Answers: 2
#1

Re: Dry nitrogen for transformer preservation

05/22/2010 12:13 PM

Can you tell us more about your 150 Million Volt Amp Transformer?

My 32KVA and 15KVA transformers are kept under CLEAR clean oil.The vent on the side will sometimes be on a vacuum.This is a small brass relief or safety valve,with a ring on the end(vent valve is above oil level)in dry air area.

I have seen the smaller of my transformers "wick" a small amount of oil,to the outside of the case.Alarming at first blush,until I remembered I had moved an electrode gasket.A slight tightening fixed it.

I am sorry I cannot directly answerer your question other than to say that there seems to be a fairly large amount of daily equalization of pressure in my large case (50KVA) transformer.This happens even without a load of any sort being present.Looking forward to hearing some speculation on this matter,as I also,find it highly interesting,and look forward to any guess/possibility of an answer.

Regards

Joe in Texas

__________________
We hold these truths to be self evident,one nation under God
Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Dry Nitrogen for Transformer Preservation

05/22/2010 4:53 PM

Something is clearly leaking here; if not the transformer, then perhaps various valves, fittings, and tube/pipe from the cylinder to the transformer. Though laborious, you might want to soap test everything.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - New Member

Join Date: Sep 2007
Posts: 1601
Good Answers: 58
#3

Re: Dry Nitrogen for Transformer Preservation

05/23/2010 7:42 AM

It seems to me that if the transformer manufacturer was confident they could build a zero leakage transformer, they wouldn't have put the bottle on it in the first place. I suspect the transformer passed a minimum leakage specification when it was built, but that specification allowed for greater than zero leakage. Very small leaks can not be detected with a soap bubble test and if the transformer has a number of these small leaks, the gas usage will add up.

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: Dry Nitrogen for Transformer Preservation

05/23/2010 1:07 PM

How long you intend storing the transformer.Normally air or nitrogen is filled for transport and air bottles are kept to make up any leakage.After receipt at site OIl should be filled up.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5

Re: Dry Nitrogen for Transformer Preservation

05/23/2010 4:16 PM

Dear guest,

Please see the Link provided, specifically section 6.2 and 6.3 of the manual. You should be aware that the relief valve will allow gasses to escape at around 7psi. If you have the pressurized tank un-regulated, or regulated above the tank relief value, you will be re-filling your tank quite often.

These are links to suppliers of automatic pressuring systems that give some additional clues as to the pressure values to be expected.

Even without energizing a transformer, it is a tank full of oil, and any tank full of oil out in the sun or in high ambient temperatures can create some very high internal tank pressures, and that will force some of the oil out around the seals. Transformers are not expected to hold a seal against high pressure.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CJMcGill (1); Judge (1); nesubra (1); Tornado (1); welderman (1)