Neutral Line

05/23/2010 12:38 AM

Is it necesary to have Neutral line in a system if you have NGR, please advice.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: neutral line

05/23/2010 3:10 AM

NGR?

__________________
Plenty of room here
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2
In reply to #1

Re: neutral line

05/23/2010 5:15 AM

To the best of my knowledge .. "NGR" means Neutral Grounding Resistor and obviously, a neutral is required.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#3

Re: neutral line

05/23/2010 6:58 AM

Answer is already in your question. It is necessary to have Neutral in a system to have NGR. You are hereby advised.

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: neutral line

05/23/2010 7:31 AM

Rather it is the other way round. If you don't have a neutral you need not have an NGR.

Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 22
#5
In reply to #4

Re: neutral line

05/23/2010 9:52 AM

NGR will be connected to the star point, could it be possible to have 3phase 4wire system.

Register to Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6

Re: neutral line

05/23/2010 3:35 PM

Ronald,

It seems that you are asking if it is OK to earth the star point, or neutral point at the source through a Neutral Grounding Resistor and then only run a 3 wire system out to the loads without including a neutral conductor. If that is your question, then yes it is electrically functional.

The effect will be current limited earth faults, reduced damage upon fault, and improved fault protection. Treat the system protection and metering as if you were supplying all 4 wires to the loads.

CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 22
#7
In reply to #6

Re: neutral line

05/24/2010 12:47 AM

thanks, another setup of question, let say i will connect the star point to NGR then to earth, is it possible to get another neutral line from star point going to load, to have a system of 3phase, 4wire.

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#8
In reply to #7

Re: neutral line

05/24/2010 1:52 AM

It is not advised. If the neutral is taken before NGR the earthfault current flow will bypass NGR, thus the purpose will be defeated.

__________________
BNDas
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #7

Re: neutral line

05/24/2010 7:50 AM

If you connect the start point to the NGR then the NGR is grounded so that you have a resistor beteen the star point and the ground.... If I understood well(?) it is OK to run a Neutral line from the start point to the loads. You will now have a 4 wire system. If a fault occurs between phase and ground the short circuit current will be limited by the NGR resistor.

If the requirement of the NGR is to limit drastically the ground - Neutral fault current, then the Neutral 4th wire can be a problem.

BUT THEN A FAULT BETWEEN PHASES IS ALSO GOING TO BE A HIGH CURRENT PROBLEM!

NGR are not normally required when grounding the star point at a transformer. You need the earth resistance to be minimum and within the norms.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9

Re: Neutral Line

05/24/2010 7:24 AM

You may find this paper informative, please download and study:

schneider-electric ect177.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#11

Re: Neutral Line

05/30/2010 12:30 AM

Dear Mr. Ronald A,

Yes. The answer is YES for your Quiery, The role of NEUTRAL is different from that of NGR.

An electrical system can be properly designed such that there will be little current flow through Neutral, but Neutral is a Must.

DHAYANANDHAN.S

CR4 MEMBER,

INNDIA.

Register to Reply
Anonymous Poster
#12
In reply to #11

Re: Neutral Line

05/30/2010 1:30 AM

where can I buy this neutral? is it available in the same shop where I bought the NGR?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#13
In reply to #12

Re: Neutral Line

05/31/2010 2:12 PM

Dear Guest,

For smaller capacity, the same wire size will work as neutral.

For larger capacity, 1/2 Core, i.e 50 % of the cable size will work as NEUTRAL CORE.

DHAYANANDHAN.S

Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Neutral Line

06/01/2010 5:26 AM

But some places, i noticed that double size neutral is used. why?

Register to Reply
Register to Reply 14 comments