Can you send me a mail thro this forum's mailbox - intimating your mail IDZ so that I can send you a complete write up on Vector Groups & its testing? I am unable to load diagrams in thie forum.
Hi, Suvo Nababarsha 1417. I've a practical way to check the vector group of a transformer. Consider Primary side phases as R, Y and B and corresponding secondary phases are r, y and b.
1. Short R-r by a copper wire.
2. Now apply 415 V(increase the voltage gradually to limit the current) in between R-Y-B.
Shuvo nobobarso.Thank you for your answer and cooperation.Can we do this by shorting any other terminals.In that case what will be the condition for being Dyn11 &
Dyn1.
apni elish mach pachondo koren.elish mach er dam per kg tay Tk. 500-600 hobey dhakai.
I've given you the example by considering R phase as reference. You can do it by considering any other phase as reference and then you have to measure voltages as I mentioned earlier, but the suffix and prefix of the equations will be different.
As Samad vai told, never apply the voltage in LV winding.
please explane me how to test victor group trans test in ynd11 and ynd1 and ynd5 and dyn1
thanks
CR4 Admin: Email address removed. Please do not post email addresses on a public forum. You can register to CR4 and communicate using the private messaging system.
Caution: Never apply voltage to the low voltage side.
Shidhu: Apni Bangla Janen?
- MS
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
dear electrical expert can u tell me how to perform the vector group test ,,,i mean how u can get the conditions for different vector groups...i.e dyn11 or dyn1 ...