Network Study

05/23/2010 8:22 AM

Hello Sir's.

Sir we are carrying out the load analysis for a network and I'm slightly confused how to proceed, please if someone can guide me, i will b very grateful to him, also any suggestion is warmly welcomed.

So, the network is feed from 30/40 MVA transformer, but its been limited to 30 MVA as per the demand of the client, but now the client wants to increase the load 40 MVA, which has been confirmed by the Power provider. the network consists of approx 110 transformers combining the total MVA of about 110 MVA, but system and the loading of the transformers has been designed like this it can only take 30MVA ( on average the transformer has been designed to carry out the 30% of their full capacities), but the max demand ever recorded is 22 MVA, so now the client wants to add another 17MVA load, I have carried out the load analysis and with minnor changes ( like changing of Ct's and relay settings) the study shows that load can be loaded.

but I'm finding it very hard to justify that the load can be loaded, and i m confused either to go with the design or the MAX LOAD ( as i told the max load ever recorded is 22 MVA , but any time in future it can be loaded up to 30MVA as well). So if some please guide me how to proceed, and what methodology should i adop, what necessary precautions i should consider, Please provide me with your kind suggestions .

Thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#1

Re: network Study ..

05/23/2010 9:48 AM

Your statement is little bit confusing. "the network consists of approx 110 transformers combining the total MVA of about 110 MVA"- Pls tell me how do the transformers are connected, parallel or series and how many buses are there? Then I can give you the correct answer.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: network Study ..

05/23/2010 3:42 PM

I don't know of any code that would allow a diversity factor as low as 0.30 or 0.40.

If several users actually use the full capacities of their individual transformers, the CB or fuses on the main transformer are likely to trip. This no doubt would irritate a bunch of people when the whole building goes down.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3

Re: Network Study

05/24/2010 1:23 AM

Your Load detail like Running, Standby, Intermittnent load, Lighting Load etc and SLD of the whole system with Transformer & Switchgear rating is required. The operation philosophy of Loads also is important for analysis.

__________________
BNDas
Reply
Anonymous Poster
#4

Re: Network Study

05/25/2010 6:33 AM

Which is make of your transformers, that is designed only 30% of capacity??...Do you mean that the system( breakers, panel board, cables) designed for 30% of capacity?

Reply