Hi,
I am working on a project(shutdown valve upgrade) that require a sil 2 loop.
given that the control system used is sil 3, solenoid valve used is sil 2, actuator is sil 2 but with a valve that is NOT sil certified, is there any chance that a sil 2 loop can be achieved?
Need some basis to argue, i think its not possible since PFD(sys) = PFD(logicsolver) + PFD(sensor) + PFD(final element), and PFD(final element) has the biggest portion.
Need your expert advice, thank you very much.