Parallel AC Contactors

05/24/2010 8:10 PM

While it may not be the best idea, I'd like to run two AC contactors in parallel and split the current between them, as to reduce costs. Any suggestions? Will this pose a problem with UL certification?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
8
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Parallel AC Contactors

05/24/2010 8:26 PM

Yes it poses a problem with UL, and no it is not a good idea.

  1. You CANNOT, no matter how clever you think you are, ABSOLUTELY GUARANTEE that both contactors will remain closed when you want them to be. As soon as one fails, the other one is instantly overloaded by 100%, ergo, fire ensues.
  2. You CANNOT, no matter how clever you think you are, ABSOLUTELY GUARANTEE that both contactors will close at exactly the same time. When one closes even a fraction of a second before the other, it will take the FULL instantaneous inrush current. Contactors are designed to handle the inrush current seen in the rating they are designed for, but not TWICE the rating they are designed for.
  3. You CANNOT, no matter how clever you think you are, ABSOLUTELY GUARANTEE that both contactors will open at exactly the same time. Contactors are made to Break an amount of current typically seen for the rating they are designed for, but not TWICE that current.
  4. You CANNOT, no matter how clever you think you are, ABSOLUTELY GUARANTEE that the current will be shared equally by both contactors. As soon as one or the other of the above conditions begins even the first inklings of degradation of the contacts, the resistance will change. Electricity always follows the path of least resistance, so when one changes, the other bears additional load / heat. That will then hasten the deterioration on that contactor and the two will race to destruction, ergo the fire ensues.

Other than that, no problem...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 8)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2
In reply to #1

Re: Parallel AC Contactors

05/24/2010 8:36 PM

GA

This kind of cost cutting is just one of the ways that electric fires get started. Oh and a final point, if in the burnt rubble an insurance investigator finds this dual contact configuration, this pseudo-electrician will be lucky to only lose their license.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #1

Re: Parallel AC Contactors

05/24/2010 8:37 PM

JRaef,

I had the same concerned, and have read in one place that if the contactors are fused, then it could be done. Proper specing would resolve 1-2 in your list. As far as equal load on both sides, it's no problem in my application.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#5
In reply to #3

Re: Parallel AC Contactors

05/24/2010 8:46 PM

have read in one place that if the contactors are fused, then it could be done. Where? To vary this far from an acceptable practice, I want to see chapter, verse and most importantly conditional details before leading somebody to a fire.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #3

Re: Parallel AC Contactors

05/25/2010 12:57 AM

Spacing has no bearing on this, I have no idea what that comment was intended to mean. It has nothing to do with spacing, it has everything to do with timing. Fractions of a second count. It may LOOK to you as if the contactors can close simultaneously, but that is virtually impossible, and that split second timing difference will make all the difference in the survival.

Re: "if the contactors are fused..." Now with this extra fusing, you have introduced a new pitfall, what if one fuse blows? Now you have created a situation where only 1 pole of one contactor can burn... even worse. To protect from that, you will have to use a voltage monitor relay on the load side of each contactor. So you then trade one large contactor for 2 smaller contactors and 2 sets of fuses and 2 fuse holders and 2 voltage monitors relays and a power splitter block to connect them and 7 devices to mount and wire instead of one... Where is the savings?

Besides, doing something wrong, then fusing it so it doesn't start a fire, is just bad engineering practice. Please do not do it.

All this said, why are you so adverse to using a large enough contactor? What size motor are we talking about here? What type of application? Because if they are to be used as a bypass arrangement for a soft starter, then it is something that people do. This is because in that scenario, the motor is ALWAYS stopped and started with the soft starter SCRs, the contactors only shunt power around them after it is already running. They are never called upon to start the motor or to stop it, so the high damaging current issues are avoided.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#25
In reply to #1

Re: Parallel AC Contactors

05/26/2010 3:43 PM

"Other than that, no problems." Tell us what you really think! Ha Ha. Buy the way GA. JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
2
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#4

Re: Parallel AC Contactors

05/24/2010 8:42 PM

Short answer, it's a bad idea, yes it will be a problem. My suggestion is that you acquire the properly rated contactor as that will save money and grief in the long run.

Cost cutting not only costs money it may cost lives...

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #4

Re: Parallel AC Contactors

05/24/2010 9:24 PM

Enough is told. What I can add is this type of cost savings (?) proposal may come from finance people, not from engineers.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8

Re: Parallel AC Contactors

05/25/2010 1:17 AM

While i agree with and appreciate the responses so far, it is well known within the industry to parallel two contacts, even two contactors for high-current, low severity duties like AC1 as per IEC 60947-4. Here is an example:

Of course, this is done by the engineers at ABB Vasteras, with lots of checks and tests. The point is that there are TWO magnets in this.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Parallel AC Contactors

05/25/2010 1:30 AM

Let me hasten to add.....such a thing MUST be done by the manufacturer, NOT by the user

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #8

Re: Parallel AC Contactors

05/25/2010 10:02 AM

If you look further, i believe you will find that these contactors are NOT rated for AC motor starting!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #13

Re: Parallel AC Contactors

05/25/2010 10:18 AM

Of course, i did say that ... AC1 duty as per IEC 60947-4 is just heating load. i did not notice any mention of any kind of load by the poster, motor or otherwise.

We now know the reason....that 200A contactors seem overpriced...but still don't know what is the load, what is the frequency of operation, are inching(jogging) and plugging involved, is it switching capacitors .. whatever. Best that the poster elaborates a bit, but all the same... NOT a good idea to parallel two contactors !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#15
In reply to #14

Re: Parallel AC Contactors

05/25/2010 10:47 AM

Also quite typical though. A new individual asks for engineering help by asking only the question in their mind but none of the relevant background information. We appropriately think of the worst case scenario, since they don't explain what needs to be known to do a proper evaluation. The worst case scenario we describe is not what they are doing so they do their foolish act anyway. All we can do is warn these fools of the consequences.

In this case, my preferred scenario will be for UL to reject this design and this individual has to explain why this rework has to be done. Short of this, I just hope nobody gets hurt.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16
In reply to #14

Re: Parallel AC Contactors

05/25/2010 1:44 PM

..." i did not notice any mention of any kind of load by the poster, motor or otherwise."

Oops, you are absolutely right! Sometimes I read things that are not there I guess.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#20
In reply to #16

Re: Parallel AC Contactors

05/25/2010 10:23 PM

Join the club

If it is any consolation, 90% or more contactor usage is for motor control. Had i not been working on a complex capacitor-switching application, i would probably have jumped to the same conclusion.

The poster now says "EV" which may mean DC motor switching, albeit at low voltage, but another complex application involving blow-out coils etc.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#10

Re: Parallel AC Contactors

05/25/2010 6:13 AM

Consider your rating of contactor(if used one) = X

rating of contactors(if used two) = X/2

It is never going to happen that the cost of 2 contactors less than single contactor. You will have additional work cost also for using two contactors. Your idea for cost saving is useless and will affect inverse.

Register to Reply
Anonymous Poster
#11
In reply to #10

Re: Parallel AC Contactors

05/25/2010 9:02 AM

Thank you all for your responses. As far as the pricing issue - I can get two 100A 600V AC contactors for less than a $100.00. A single 600V 200A contactor is around $500.00. There is a huge price jump for contactors above say 120A. Again, thank you all!

Register to Reply
Anonymous Poster
#12
In reply to #11

Re: Parallel AC Contactors

05/25/2010 9:22 AM

Does not make sense. However, which is the brand and make of those contactors?

Register to Reply
Participant

Join Date: May 2010
Posts: 2
#17

Re: Parallel AC Contactors

05/25/2010 2:54 PM

You all need to relax, no one is designing anything yet. I was asking for some general comments on the subject because I read in an EV application where someone had connected contactors in parallel.

I hope you all realize that exploring your options is an essential part of the design process; jumping to conclusions like a bad girlfriend is less than appealing.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#18
In reply to #17

Re: Parallel AC Contactors

05/25/2010 4:47 PM

Sometimes posting MORE information is better than less...

If the contactors were on the supply side of a DC input drive, then the induction / inrush issues would not matter because the drive would likely be in an Off state when the contacts close or open, you could probably get away with it.

By the way, $500 for a 200A contactor in an OEM context... someone is making a killing! If you are looking at 48VDC, you have a LOT of low cost options available to you. Make sure you are not basing your assessment on a standard industrial AC contactor; A) it may not have any appreciable DC rating on it at all, and B) it is not likely to be attractive as far as real estate goes.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#19
In reply to #17

Re: Parallel AC Contactors

05/25/2010 4:49 PM

Relax you say. Well excuse me for showing concern. Apparently unlike you, I worry about people seeing a dangerous proposal getting any kind of approval.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#23
In reply to #17

Re: Parallel AC Contactors

05/26/2010 1:51 AM

Ah ha .. i think this is where you saw this : ssinc .. yes? if so, even that thread discourages this paralleling.

However, i agree with you that one should explore all avenues, even those which appear at first sight to be ridiculous. That is what brainstorming advocates. Good luck to you.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#21

Re: Parallel AC Contactors

05/26/2010 12:24 AM

Hi,

The cost of contactors will go up. In case if any one of the contactor fails to operate

the entrie system fails. So it is not advisible for rugular operation. For limiting the starting current it is OK

N.Prabakaran

Register to Reply
Commentator

Join Date: Nov 2008
Posts: 80
Good Answers: 4
#22

Re: Parallel AC Contactors

05/26/2010 12:41 AM

Check out vacuum contactors. They are cheap compared to regular contactors. In the larger contactors, they were cheaper that a set of new contacts for regular starters. We used a lot of them to replace large contactors and they were much more reliable. For maintenance, the stroke of the contactor should be checked once a year, it takes about 5 minutes.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#26
In reply to #22

Re: Parallel AC Contactors

05/26/2010 4:36 PM

May I ask where I might purchase an inexpensive vacuum contactor rated for 600v 150 HP AC3?

I have been looking for one for about a year now and they are very expensive ( compared to a standard), even used, on Ebay.

__________________
CRTL-Z
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#24

Re: Parallel AC Contactors

05/26/2010 5:07 AM

Well Ed

You've won the prize....... you get the cigar!

As much as I don't want to be harsh... I find myself having to comment.

What a dumb idea!!!!!

Please tell everyone it is just an idea and you haven't done it!

Please. please read ALL the answers..... and DON'T do it!

cost of two contactors = $500 (maybe) plus cost of fire that follows and damage to buildings/plant and then no further insurance = $25,000,000 (add as many zeros as you like)

Cost of ONE fit for purpose contactor = $1,500 (maybe more)

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#27

Re: Parallel AC Contactors

05/26/2010 9:40 PM

Sir,

I agree fully with the NO answer as given by JRaef. For a number of years, I worked in a U/L electrical panel shop. Any application such as what you suggested would have to be fully within the application design and U/L listing of the manufacturer's contactors, or be tested and certified to U/L standards on your design. I don't think that either of these is feasible or likely to succeed. If, however, the contactors were to have a common mechanical actuator for all sets of contacts, then it may be remotely possible for such a combination to pass the required tests and receive the required certification/listing.

Probability of this one flying???--less than 0.01%.

--John M.

Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); brich (1); Circuit Breaker (1); ed.diggs (1); jmueller (1); JRaef (5); kvsridhar (5); msamad (1); redfred (4); Tobugrynbak (1); Unredundant (1); vtbgiraud (1)