Previous in Forum: Electric Tester   Next in Forum: DIESEL GENERATOR NOT GIVING OUTPUT VOLTAGE
Cable Current Carrying Capacity
05/26/2010 10:15 AM
Chart of current carrying capacity of power cable with derating factors.
Re: Cable current carrying capacity
05/26/2010 10:32 AM
British Standard 7671.
Good Answers: 244
05/26/2010 10:55 AM
If you are in NEC world, use Table 310.16 to 310.20 (page 70-148 to 70-152 of NEC 2008). These tables also have the derating factor for the ambient temperature correction.
- MS
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member
Re: Cable Current Carrying Capacity
05/26/2010 12:10 PM
Samad vai, it will be better if you can give or mention those tables in this forum.
Good Answers: 244
05/26/2010 2:16 PM
I would suggest you to buy the NEC code (NFPA 70). See http://cr4.globalspec.com/thread/51102 for the links for all other electrical standards. However, I found a pdf document in a website, it has the NEC ampacity tables and other good staffs for the cable selection (the NEC ampacity Table 310.16 to 310.20 are almost at the end of the file).
- MS