05/27/2010 12:14 AM
diesel generator not giving output vltage.what may cause it since all gauges showing correct parameters.maybe the relay does not trigger the generator to put output voltage?
Re: voltage problem in diesel generator
05/27/2010 12:50 AM
what is that relay put output voltage? all gauges showing parameters. Do you have voltmeter?...what is the reading?...how did you check the voltage?...RPM is correct?...
05/27/2010 2:57 AM
yes we have voltmeter and rpm gauges and its normal (value is 220v and 1800 rpm 50hz )
05/27/2010 1:27 AM
CHECK YOUR AVR IF YOU KNOW WHERE IT IS SITUATED ON THE GENERATOR OTHERWISE CALL SERVICEMAN
DO YOU HAVE A VOLTMETER ON THE GENERATOR AND IS READING NO VOLTAGE?
THANKS,
JOSEPH
05/27/2010 3:00 AM
we have voltmeter and its reading is ok.the genset is connected to an ats.the problem is when transferring the load to the gensett does not give output.do you think its avr problem or control relay
05/27/2010 5:26 AM
at no load developing the voltage, whn ever connecting the loads , voltage become zero,it is seems to be the faulty AVR.
05/27/2010 5:24 AM
You can check the AVR.
05/27/2010 7:48 AM
Thanks everybody. Problem solved now. The breaker was off. I will come back again, for such big issues in future. Thanks a lot
05/27/2010 9:11 AM
You have GOT to be kidding me!
You have asked the same question at least three (3) times. And after all of that, the breaker is tripped.