Circuit Breaker

05/28/2010 3:02 AM

What is antipumping feature in a circuit breaker ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Circuit Breaker

05/28/2010 3:58 AM

anti pumping ---available in google search. if you mean aunty pumping????.....

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Circuit Breaker

05/28/2010 4:54 AM

IEC 60947-1 definition 2.3.20:

A device which prevents reclosing after a close-open operation as long as the device

initiating closing is maintained in the position for closing.

However, there is no separate 'device' as such in modern CBs. The mechanism is so designed as to take care of this. Electrical antipumping is also offered by some, by giving a momentary closing command even if the input is a sustained command.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#20
In reply to #2

Re: Circuit Breaker

01/27/2012 12:38 AM

When a LOR is used will the anti-pumping relay be bypassed?.

__________________
pnaban
Reply
3
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#3

Re: Circuit Breaker

05/28/2010 5:22 AM

A circuit breaker has seperate closing and tripping solenoids.Once the CB is closed through local/remote close command,it should trip only when a trip command is given through the CB Control switch or through a protection relay/master trip relay.

In some cases, the CB may trip immediately after it is closed due to any fault condition occuring at that instance.If the closing command is maintained inadvertently/intentionally,the CB will close again and the "closing-tripping" cycle will recurr.This is called pumping ,which is a nuisance and reduces the life of the CB .The device /scheme provided to prevent this unwanted phenomenon is called antipumping feature.It can be a mechanically in-built feature as per the manufacturer's standard.This can also be achieved electrically by introducing an anti pumping relay (an auxiliary relay) in the closing circuit of the CB which picks up after the CB is closed and blocks the close command through it's NC contacts.

Hope,this answers the query.

S PRADHAN

__________________
Learning is a never-ending process.
Reply Good Answer (Score 3)
Active Contributor

Join Date: Aug 2008
Posts: 11
#4
In reply to #3

Re: Circuit Breaker

05/28/2010 6:18 PM

I agree, but I have seen electrical anti pumping relays which also cut off the closing circuit even if the circuit breaker fails to close. The concept is that the anti pumping relay is energised simultaneously with the close signal to the CB close coil, but it has a time delay before it cuts the closing circuit. I guess the idea is also to avoid continuous energisation of the closing coil in the event of a stuck breaker.

__________________
Opportunity is missed by most because it is dressed in overalls and looks like work
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Circuit Breaker

05/28/2010 10:13 PM

This was necessary when closing solenoid coils were short-time rated and were susceptible to burnout if the supply was continously given, and the CB failed to close (a NC contact of the CB was used to cut off supply to the closing coil). However, modern trend is to have closing/shunt/undervoltage coils which are electronically controlled, and, as i mentioned before, the closing (and shunt-trip too) coils get a momentary (say 50ms) command, even if the incoming command to close (or trip) is a sustained one. This saves a couple of aux contacts of the CB and also, in the case of the closing solenoid, gives electrical antipumping.

Mechanical antipumping, which is the best way, is achieved by a nice "escapement" system in the closing linkage.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#6
In reply to #5

Re: Circuit Breaker

05/29/2010 1:00 AM

You are right.But, an electrical antipumping scheme should also be provided to serve as a back up since, mechanical "escapement" in the closing linkage may fail due to obvious reasons.Further,mechanical arrangement being an in-built feature of the CB,user has to depend on the manufacturer in case of any mal-function; whereas, he can easily rectify the electrical scheme if required.Hence, we recommend the electrical antipumping scheme to our clients.

__________________
Learning is a never-ending process.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Circuit Breaker

05/29/2010 8:37 PM

i appreciate your viewpoint, and i believe in providing redundancy where safety is concerned. However, i would urge you to study the escapement design of the following LV CBs..... Schneider Electric's MASTERPACT, ABB's EMAX and CS Electric's WiNmaster. There is negligible or no chance of failure of the escpement. Anyway, the microprocessor-controlled closing coil gives electrical anti-pumping too as a backup in case of the CS Electric ACB,

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#8
In reply to #7

Re: Circuit Breaker

05/31/2010 2:12 AM

Thanks a lot.I would certainly like to study the suggested litreature.Can you please provide relevant links ,if possible,for my reference as well as for benefit of the forum?

Regards.

S PRADHAN

__________________
Learning is a never-ending process.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: Circuit Breaker

06/01/2010 11:27 AM

Dear Mr Pradhan, i had not forgotten this .

Just that i was searching for some links which mention this. Regrettably, nobody does. i also have many patents of various companies, and again, there is no specific mention of this antipump feature. Nevertheless, this feature is avaialble in almost all modern LV ACBs. i am afraid that a video of a CAD simulation will be the best way to understand. i am willing to send this to you, and answer the queries you will have on it. i will try to send the video clip through the CR4 mail system.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10
In reply to #9

Re: Circuit Breaker

06/02/2010 9:19 AM

CR4 mail system does not allow attachments. So, i am giving here some images which may be enough to explain the action :

(This is my own design, and has no IP issues )

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#11
In reply to #10

Re: Circuit Breaker

06/03/2010 2:35 AM

Wonderful design!Nice images!!But,I'd still prefer to go for an electrical antipumping scheme as aback up to this in-built mechanical antipumping feature.

__________________
Learning is a never-ending process.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #11

Re: Circuit Breaker

06/03/2010 4:35 AM

Thanks.

Lay me understand the requirement of antipumping:

What does a complex antipump scheme do? It prevents reclosure of the CB after ONE closing operation. Right?

In my design, the closing coil gets only ONE pulse of 50 milliseconds. No matter how long the closing command is maintained.

So i submit : (a) i have mechanical antipumping which functions even if an operator holds the closing pb in depressed position for a long time. Also works for an electrical command through the coil and (b) i have a microprocessor-controlled closing coil which operates ONCE per closing pulse. If i have to close the CB again, i need to switch OFF the closing command, so the pcb re-arms itself, and then re-apply the closing command.

In fact my deisgn prevents closing of the CB if (a) there is trip command already present and (b) if the CB is already on. Not unique, everyone in LV ACB field has it.

Now, it is possible that i am unaware of some other feature that is offered in an external antipump scheme. i would like to know more, please respond, thank you.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: Circuit Breaker

06/03/2010 4:57 AM

OOPS..horrible typo ... "Let me understand ... " sorry. Must wear my reading glasses

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#14
In reply to #12

Re: Circuit Breaker

06/05/2010 1:33 AM

I sincerely honour your expertise & experience in the field of LV ACB design. You need not doubt your fundmental knowledge base.But you will appreciate the fact that,the life of any mechanical device is poorer than it's electrical counterpart.The actual user's(who runs and maintains the system/equipment )confidence level is an important criterion for selection of the concerned equipment/system.Particularly, when it serves a production shop in which, availability of shutdown for routine maintenance is very rare.The PSU client we are working with, does not mind investing more on back ups,back ups to back ups,redundancies etc since , any loss of production due to outage of power supply ,will offset the savings made on account of non-provision of back ups.

Hope ,this satisfies

__________________
Learning is a never-ending process.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #14

Re: Circuit Breaker

06/05/2010 3:57 AM

Thank you Mr Pradhan, you have hit the nail on the head. Backups. Redundant protection. i have no argument against it, just wanted to be sure i have not missed some aspect of anti-pumping systems.

However, it may be interesting for you to know one aspect of controlgear that i had to address in several user fora.

You know that reversing and star-delta contactors need to be interlocked to prevent dead-short-circuits. All good manufactirers offer mechanical interlocks between contactors for this purpose. For the last 40 years off and on, i have been trying to convince customers to use the mechanical interlock in addition to the electrical interlocking they do normally, using auxiliary NC contacts of the contactors. More than 90% are unwilling to spend the extra money for this mechanical interlock saying that their electrical interlocking is enough.

i normally carry a dismantled aux contact block and ask such customers:"are you trusting your interlocking to this rather flimsy piece of brass which can weld shut sometimes?" i am happy that i am able to convince most customers to use mechanical interlocks also.

Sorry for the long post, but i realise you are my kind of person, and will appreciate the finer nuances of switchgear and safety

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#19
In reply to #5

Re: Circuit Breaker

01/27/2012 12:33 AM

In locations where a LOR is used will the anti-pumping device be bypassed?.

__________________
pnaban
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#21
In reply to #19

Re: Circuit Breaker

01/27/2012 12:38 AM

Er...what is an LOR? Sorry for my ignorance.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#22
In reply to #21

Re: Circuit Breaker

01/27/2012 5:14 AM

Some commonly used abbreviations are: EFR-earth fault relay,OCR-over current relay,LOR-lock-out relay,UV-under voltage,OV-overvoltage, ELCB,earth leakage CB,RCD-residual current device and so on. I wonder whether different countries use different abbreviations

__________________
pnaban
Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#23
In reply to #22

Re: Circuit Breaker

01/27/2012 6:03 AM

i am sure different countries use different acronyms, and even in the same country, one acronym may mean several, widely different things. Best to avoid acronyms.

Thanks for the clarification. What does a lock-out-relay do?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#25
In reply to #23

Re: Circuit Breaker

01/31/2012 8:33 AM

In power lines or cables when a fault occurs the CB trips but to guarantee security of supply they incorporate a AR(auto-reclosure)relay to switch it on automatically 2 or 3 times and if fault persists it will lock-out. Then someone should inspect and clear the fault and manually reset the LOR and switch on the CB. This is useful in case of transient faults like a branch of a tree or banana shoot touching the over head line due to the blowing wind.

__________________
pnaban
Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#24
In reply to #19

Re: Circuit Breaker

01/27/2012 6:51 AM

Somewhere on this page, there is an excellent explanation of why a lockout relay cannot replace an antipump relay. Excellent link provided by vinodh on another thread...

http://electrical-engineering-portal.com/anti-pumping-and-lockout-relays

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#16
In reply to #3

Re: Circuit Breaker

06/05/2010 4:17 AM

Incidentally, this comment had received 2 votes for GA, but one vote against ! i wonder why? So, i voted GA to countermand that... you deserve a GA for it

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: Bhilai,Dist.-Durg,Chhattisgarh,INDIA
Posts: 104
Good Answers: 5
#17
In reply to #16

Re: Circuit Breaker

06/05/2010 6:42 AM

Thank you Mr.Sridhar for the compliment.I feel, the system of voting in the forum has inherent lacuna.There is no mechanism to block mindless voting by some member/person who has not understood the question/answer/subject at all.It is somewhat similar to the voting by any Tom, Dick & Harry (ie.Aam Janata) for the participants of popular TV shows like "Indian Idol" or other musical shows irrespective of their level of knowledge in the concerned field ,which results in elimination of some deserving participants.

Hope,concerned Authorities of globalSpec Inc will look into this and do the needful in future.

__________________
Learning is a never-ending process.
Reply Off Topic (Score 5)
Member

Join Date: Feb 2011
Posts: 9
#18

Re: Circuit Breaker

06/27/2011 12:37 PM

Here's the link for EMAX breaker section from ABB low voltage product selection guide.

http://www.clrwtr.com/PDF/ABB-Controls/ABB-Emax-Power-Breakers.pdf

Reply
Reply to Forum Thread 25 comments