Transformer Cooling Method at 12MVA

05/28/2010 3:27 AM

I have observed that above 25 MVA to say 50 MVA, the transformer cooling methods for 11/220kV are ONAF.

But what could be the cooling method for my off load tap changer transformer at 12MVA, to be used with generator in a unit connected scheme (of vector group YNd11) in a hydropower station of say 60 MW capacity with 3 generating units?

Regarding the type of load, it is a peaking run of the river type of plant, and will be run 10% continuous overload for 3 months during wet periods.

Saurav.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Transformer Cooling Method.

05/28/2010 3:55 AM

howmany types of cooling methods you know actually? you can ask any type for manufacturer. or they will suggest according to their product specification.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#2
In reply to #1

Re: Transformer Cooling Method.

05/28/2010 4:43 AM

Normally there are 3 types as follows.

1 ONAN

2. ONAF

3. ONWF

4. OFWF

But if there are more than one MVA rating for the same transformer, then there can be stages of cooling like ONAN/ONAF etc.

Do u have any comments?

sks

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Transformer Cooling Method.

05/28/2010 9:15 AM

There is some discussion about the selection of transformer cooling method (ONAN or ONAF) and transformer ratings in the previous thread http://cr4.globalspec.com/thread/43826. You can look into it for further help.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#4
In reply to #2

Re: Transformer Cooling Method.

05/28/2010 9:37 AM

Hi,

How do you synchronize your generator to grid? Do you use a autosynchronizer?

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#7
In reply to #4

Re: Transformer Cooling Method.

06/28/2010 4:23 AM

actualy i only have knowledge about synchronizing genreators in paralle, i.e. lamp bright synchronizing.

i think, for a unit connected scheme, where a hydrogenerator is connected with transformer, and only then connected to circuit breaker to bus. Here, the cb is also called synchronizng breaker, because it connects generator part to load part i.e. bus part. We also have autosynchronizer, but how we do it manually - taking care of voltage, phase, phase sequence and frequency?

regards,

Register to Reply
Associate

Join Date: Feb 2010
Posts: 40
#5

Re: Transformer Cooling Method at 12MVA

05/29/2010 5:38 AM

hi

It is mentioned on Transformer Name plate. If not mentioned better to ask manufacturer.

Generally 12 MVA generator transformers ONAN or ONAF.

ONAN - Oil natural air natural - This is like natural air cooling

ONAF - Oil natural forced air - In this condition fans are connected to transformer radiators and operating according to set temperature.

I hope this helps to you.

Regards

Hanu

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#6
In reply to #5

Re: Transformer Cooling Method at 12MVA

06/25/2010 3:40 AM

Hi.

Looks like OFWF could be loaded to 167% to that of ONAN/ONAF of same rating.

sks

Register to Reply