Electric Motor - 40hp / 4 pole / 3 phase

05/28/2010 6:49 AM

I have rewound a 40hp 4pole 3phase motor. The no-load current is 6amp on Star and 35amps on Delta. I think something wrong as the delta current is on the higher side. Can i rewind it again by using HALF size smaller wire and increase by two turns turns??Your help will be very much appricated. Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/28/2010 1:32 PM

Something it wrong with your math or your typing.

40HP and you think 35A is too high?

40HP @ 460V should be around 52A

40HP @ 575V should be around 41A

Are you at 1000V or something?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/28/2010 3:56 PM

The voltage is 420;

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #1

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 6:55 AM

He said NO LOAD current ! (it is high!)

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#3

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/28/2010 11:08 PM

40 HP is rated load. No load current should be less than full load. If you are in to rewinding motors I expect that you CAN rewind it again using half size smaller wire an two more turns turns!!

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #3

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 6:59 AM

Why doesn't he stick to the original wire size that came with the motor in the 1st place? Obviously, he must be repairing the winding after a damage!?

Changing the wire size will affect the performance of the motor to differ from the original rating: Unless he wants to change the Motor's rating...

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#10
In reply to #6

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 11:07 AM

CAN is not the same as SHOULD. I answered the question AND you are correct.

Register to Reply Score 1 for Off Topic
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#4

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 12:08 AM

What is your winding configuration and voltages applied? Are you using series and parallel configuration? or what?

You cannot use 420V in delta from star if you have only 3 windings.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7
In reply to #4

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 7:01 AM

Why not!

If the ends of the 3 phase windings are brought out, you will have 6 ends and 3 windings (Schematic), which will allow Star Delta.

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11
In reply to #7

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 11:35 AM

Why not!

Because 420V star if conected as 420V delta will burnout the wndings, unless he has split phases wich can be configured in series or parallel, which was why I asked the question.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 7:10 AM

Check that you have rewound it correctly with the same wire size and same number of turns that were there originally. Also, the direction of the winding(coiling directions) since this is a 4 poles, each phase has 4 coils wound alternatively (direction of coiling changes...), therefore, you have 12 coils.

If you make any mistake in the direction of the coils, you will have anomalies in the current (performance) of the motor. Anomalies are not only due to the size of wires etc.

I presume that you have some experience in rewinding electric motors, therefore you should know most of the above, unless this is the 1st time.

Register to Reply
Anonymous Poster
#9
In reply to #8

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/29/2010 7:32 AM

Thank you for the response. Actually i rewound the same way as it was but the motor had been reewound previously by someone else. That is why i think the windings were not right. It is 12sets 2 coils per slot, group of 4 coils, 48slots.

Register to Reply
2
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#12
In reply to #9

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/30/2010 8:23 AM

first thing to do

please give following information

  • stator length (mm)
  • rotor outside diameter (mm)
  • number slots (48 ?)
  • two layer winding (2 coils per slot)
  • actual wire diameter, number of wires parallel, number of groups parallel
  • copper wire or aluminium wire ?
  • coil span (1 - 13 and 4 coils in series per group ?)
  • actual number of turns per coil

motor nameplate data

  • voltage 420 (is this 420Delta or 420 star or is this a double voltage motor 210/420V ?)
  • current at full load
  • frequency 50 or 60 Hz
  • cos fi
  • if possible efficiency

second thing to do

calculate the full load current per square mm copper surface. This should be 6 till 8 A/mm2.

if not correct, winding data will be corrupted.

connect the motor to a variable 3 phase voltage and adjust the voltage that the no load current will be 30-40% of full load voltage. In this case you have an idea for what voltage the actual winding is.

(A variable voltage you get from a three phase variac or step down transformer)

Take a look at the rotor. Are the rotor bars in good shape ? no loose rotor bars ?

Did someone put the rotor an a lathe and changed the outside diameter ?

Give us the actual winding data and we will check these against similar winding data.

Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Jan 2009
Posts: 23
#13
In reply to #12

Re: Electric Motor - 40hp / 4 pole / 3 phase

05/30/2010 8:55 AM

Thanks v much, i will post the details soon. The span is 1-11 group of 4.

Register to Reply
Register to Reply 13 comments