water cooled condenser

05/28/2010 8:08 AM

In my bar I have a carrier water cooled condenser. Its suppose to be more efficient but my water bill is outragous. Can someone help?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: water cooled condenser

05/28/2010 11:43 AM

1. Once-through water cooled condensing gives the lowest condensing pressure and hence least compressor horsepower.

2. Evaporative condensing of the type where refrigerant goes through the condenser requires somewhat more compressor horsepower, and would entail some repiping of the refrigerant circuit.

3. Combined condensing, which retains the existing condenser but then recirculates the water through an evaporative cooling tower, is higher yet in HP consumption. But the refrigerant circuit remanis unchanged.

Methods (2) and (3) continue to use the amount of water that is evaporated, plus a similar amount that is bled off to prevent concentration of minerals. But the amount of water needed is much less.

4. Air cooled condensing, like (2), also requires repiping and results in the greatest HP usage of all these methods. But it eliminates the water usage, unless the higher condensing temperature then requires oil or head cooling for the compressor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: May 2010
Posts: 3
#2
In reply to #1

Re: water cooled condenser

05/28/2010 2:19 PM

so it is absolutely necessary in order to get maximum efficiency you must have a cooling tower to complete the system. Why would some one install this unit without a cooling tower and just have water running to the drain?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: water cooled condenser

05/28/2010 4:57 PM

As mentioned in (1) in post 1, this is the most energy efficient choice because the condensing temperature/pressure is lowest. At one time, water costs may have been low enough to make this unequivocally the best option. However, if water costs go high, then a review is indicated--as an economic efficiency issue.

Hershey Chocolate is located on a creek in Pennsylvania. Originally their water usage from the creek was free, but it warmed up the creek water. When this became understood as an environmental problem, they were obliged to switch to another type of condensing. I think this entailed the upsizing of a number of large motors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: May 2010
Posts: 3
#4
In reply to #3

Re: water cooled condenser

05/29/2010 3:22 PM

Thanks!!

Register to Reply