kA Rating of Bus Bar More Than 50kA

05/31/2010 12:27 AM

if we copper considering bus bar with dencity 1.6per sqmm then it withstand 50ka as per standerd if we rquired 70ka then what may me be the disity

Vijay

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: May 2009
Posts: 40
Good Answers: 1
#1

Re: ka rating of bus bar more then 50ka

05/31/2010 2:53 AM

(I/A)2*t =.0297log( t2+234/t1+234)

I is short circuit current in amp

A is conductor area in circular mills

t is the time of short circuit in second

t1 is operating temperature

t2 is max short circuit temperature

hope this will help

Reply
Anonymous Poster
#2
In reply to #1

Re: ka rating of bus bar more then 50ka

05/31/2010 8:53 AM

If the conductor area in mm2, this formula will work?...please help me

Reply
Associate

Join Date: May 2009
Posts: 40
Good Answers: 1
#3
In reply to #2

Re: ka rating of bus bar more then 50ka

05/31/2010 10:37 PM

change mm2 into circular mills and use this formula ,if you still find problem than feel free to ask me...........