I have an application where we have the need for 2000W strip heaters in a machine. Currently the designer is using 480V 1 phase to feed the heaters, so 2 lines off of a 3 phase feed. The problem is, the feed is in one room and the machine in another, so we have to add a local disconnect switch per code. We already have a 3 pole disconnect for a small 460V motor, so now we are having to add another. Normally not a problem except there are almost 100 machines!
I have proposed they use a 277V feed to each heater. It means more current of course, but it also means we can add one more power pole to the existing 3P disconnect switch rather than an entire new disconnect (and associated conduit etc.). I also added that the heater loads be divided up as equally as possible between the 3 phases, although we have no way of controlling which one comes on and off with relation to the ones next to it etc.
The designer has questioned my idea because he feels "The Neutral current from all those machines will be too high!". As I understand it, the Neutral current would not be any more than the highest phase current, anything else will cancel each other out. Any imbalance created by the random on-off nature of the individual heaters might be problematic however, so I don't know how that would factor in. Any ideas?