Connecting Three Generators In Series

06/02/2010 10:30 AM

Dear All,

Please I have a little challenge here.

I have Three (3) different rated generators (11oKVA, 200KVA and 500KVA) Gen sets to be connected in series using ABB EK Series block contractors. The Generators will be selected using a 3-way Rotary switch.

Please can anyone assist me with a guide me on how to connect this Generators better without the use Automatic Transfer Switch (ATS) due to budget.

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Connecting Three Generators In Series

06/02/2010 11:06 AM

First, connect them in parallel rather than series.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2

Re: Connecting Three Generators In Series

06/02/2010 11:17 AM

I was also perplexed a bit, but then Tornado answered, so my thinking seemed right after all... they need to be in parallel, otherwise ALL of them need to be on all the time, right?

So each generator output is switched using the 4-pole EK contactor of appropriate rating. The coils of each of the contactors is wired through the 3-position selector switch to the appropriate control supply. Any one only will be on at a time.

So, is this what you mean? Or, are they really in series?

If you want to change from one generator to another, where will the contactor control supply come from? Not from the generators, since the contactor will drop off once that generator is switched off won't it? You may need a battery supply for this, which means you must specify the EK contactors with DC coils...they are available.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#3

Re: Connecting Three Generators In Series

06/02/2010 11:37 AM

You have budget for Generator but not for ATS??...It is like you buy car but no budget for Tyre....I have no comment about your series connection.

Register to Reply Score 1 for Off Topic
Anonymous Poster
#4

Re: Connecting Three Generators In Series

06/02/2010 5:54 PM

You must set the droop characteristic of the mechanical governers to the same value. Doop is the diff in rpm between no load and full load divided by the rated rpm; usually a percentage of 2 to 5%. This means that the individual gensets will share the load according to their ratings.

Similarly the voltage regulators need to be set to share the reactive load. This depents on the type of regulators fitted - need to consult the manuals

Register to Reply
Member

Join Date: Jun 2010
Posts: 6
#5

Re: Connecting Three Generators In Series

06/02/2010 10:42 PM

Please don't start generators when armatures are in series. You may buy three more.

Hook them in parallel with all the required devices such as frequency meters, voltmeters etc...

I have no idea what the selector switch is for. Oh yeah, a suicide knob.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: Connecting Three Generators In Series

06/02/2010 11:12 PM

I'm not sure about the rotary switch, either. I doubt that it is switching output power from the generators. More likely it aligns the synchroscope (or synchronizing lights) according to the incoming generator. [?]

A least-cost system might use manually closed shunt-trip circuit breakers for each generator, with synchronizing lights in lieu of a synchroscope. I have operated paralleling switchboards of either type, but too far in the past to be an expert.

Some further detail on this system might help.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#7

Re: Connecting Three Generators In Series

06/03/2010 1:36 AM

You mean neither serie nor parallel connection I guess, you want to supply your load from one generator at a time. if so, You may use the 3 ways rotary switch to energize the coils of your EK block contactors, with electrical interlocking between the 3 contactors, use normaly closed auxiliary contacts to prevent a contactor to close while any other is closed, you need two NC contacts on each contactor. your system still not 100% safe as there is no mechanical interlock between the contactors.... for your safety and safety of your equipment invest little more in an ATS ............... for the supply of coil, either you use an externel source as batteries as one poster suggest, or in lack of funds as it is the case, you can energize each contactor from a phase of corresponding generator before the contactor input Good luck and be safe

__________________
dont say it, write it
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#8

Re: Connecting Three Generators In Series

06/03/2010 3:15 AM

Better you connect the generators in parallel. As per condition of load, you can run one generator individual or in parallel( one or two) .

__________________
Manindra
Register to Reply
Anonymous Poster
#9

Re: Connecting Three Generators In Series

06/03/2010 4:12 AM

Oh,..man.,.. You already hired ABB EK series contractors for connection works. They will do it.

Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#10

Re: Connecting Three Generators In Series

06/03/2010 12:50 PM

A person in a proper frame of mind knew that the generator outputs need to be paralleled / phased with one another for proper operation. It can be done using 3 sets of switching contactors, where the # of contacts for each contactor are determined by the # of output phases). The option of putting the generator on line, one by one or any combination thereof via a selector switch need a little bit of modification. Assuming all contacts are properly rated for both the relays and the contactor's current carrying capacities, it is possible to configure such set up. By individually controlling each contactor coils via another set of relays contacts where the relay coils are in turn switched by the rotary selector switch. i.e., rotary position 1 will switch the first gen., pos # 2 will add gen 2, etc. It is also possible to initially select a generator with a different capacity to match load requirement or a diff gen combination via this rotary switch, which will be limited only by the number generators and the # of available switch positions.

__________________
vsar
Register to Reply
Register to Reply 10 comments