Frequency Change Between Customer Supply & Equipment

06/05/2010 2:26 AM

What is the effective solution for changing voltage & frequency between the customer supply & equipment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Frequency change

06/05/2010 2:33 AM

Voltage change: transformer.

Frequency change: VFD or motor-generator with suitable drive ratio (typically 5:6 or 6:5).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jun 2010
Posts: 2
#2
In reply to #1

Re: Frequency change

06/05/2010 2:45 AM

On what concept is a motor-generator working

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Frequency change

06/05/2010 6:50 AM

mechanical-shaft coupling concept

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Frequency change

06/05/2010 12:09 PM

The frequency depends on the rpm of the generator and the number of its poles; rpm = 120 x Hz/npoles, where n is even. As a result, 60-Hz generators run at 3600, 1800, 1200, 900,... rpm; whereas 50-Hz generators run at 3000, 1500, 1000, 750,... rpm.

To convert frequency mechanically, you can use a motor whose rpm is in one of these series to drive a generator whose rpm is in the other. They could be connected via a gear or belt drive of appropriate ratio. Such a combination is called a motor-generator.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#5

Re: Frequency Change Between Customer Supply & Equipment

06/05/2010 10:45 PM

The short answer is www.aseapower.com product choices up to 500 KVA power capacity. Smallest is about 18KVA. Custom sizes may be possible.

Tell them what voltage, frequency, phases input and they will provide suitable output according to your needs. their products are used world wide to convert shore power to whatever is needed on board a ship.

__________________