The problem with indoor earthing pits is that they must be kept damp. So, you'd need to establish a test procedure to test and maintain proper conductivity of the soil.
The controlling document would depend on where the pit is located. Country, I mean.
Maybe the pit shown below, could serve a dual purpose, properly vented to the outside, of course.
The country was Srilanka.The electrode was outdoor.If the test spike didnot penetrate the original soil but sits on recently filled earth will the reading be high after a drought? Will the problem be solved by using longer test spikes? The manufacturer didnot recommend any other method or procedure.Which reading should be used for fault calculations?
Thank you
Spam: This post was deleted because it
contained advertising outside the Commercial Space forum. Please review
Section 14 of the CR4 Site FAQ about
advertising.
Indoor could lead to dangerous situations if not done carefully under fault conditions.the step , touch pottentials will have to be below limits.Indoor earth pits are Normally not allowed .
__________________
To avoid crticism do nothing,say nothing,be nothing
In Gulf region basically not allowed an indoor earthing system. In our Gunnery simulations bldg are equiped with grounds mats but earthing hook-ups are extended to outside of the building tapped to the counterpoise earthpits at least 2.5m away from the building structure