Positive Air Pressure Calculations in a Room

06/07/2010 3:16 AM

To calculate air balance to maintain positive pressure in room.

__________________
Best Regards, Shivaram
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Positive air pressure calculations in a room

06/07/2010 3:23 AM

I can't see any point in trying to calculate such a thing. (But I am a cat)
Measure it*, if you are building a clean room facility then a few 'order of magnitude calculations' may be possible, but I expect you'd want to design in redundancy and overcapacity anyway.
I'll bet the final set up is adjusted empirically probably by throttling the outgoing air.
If you insist on trying to calculate it you would need the performance data for the blower and the leakage and volume of the room.
Del

* A U tube manometer with one limb either side of a window in the room would be simplest.

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Commentator

Join Date: Jul 2008
Posts: 63
#2

Re: Positive air pressure calculations in a room

06/07/2010 7:05 AM

Positive pressure in operation theaters, ICU and burnt patient ward are very critical for avoiding infections. Ashrae - application-chapter 7 page 8 health care facilities on table 3 specify the pressure requirements.

As a thump rule every 100 CFM of air difference between supply air and exhaust gives 10 pascals pressure inside the room. For example, in an operation theater, if supply air is 2000 CFM and exhaust is 1800 CFM, inside will have 20 pascal positive pressure. Care should be taken to monitor inside pressure as the exhaust used to be a direct drive fan whereas the supply fan used to be belt driven. In case of belt slackness and dirty air filter supply air to room will be reduced whereas exhaust will remain constant thereby chances of reduced inside pressure or negative pressure. The exhaust fan should be electrically interlocked with supply fan in such a way that exhaust starts after some time lag of supply fan started to avoid initial negative pressure inside.

Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#3
In reply to #2

Re: Positive air pressure calculations in a room

06/07/2010 11:51 PM

The problem with using a "rule of thumb" is that it does not consider the actual volume of the room or total supply air volumes.

As stated earlier by The Cat, several unknowns regarding room tightness, etc. are in the way. If you have a facility that was built as air-tight as practical, you still want to be reasonably safe.

Assume that 75% of your "pressurization" air will be lost through cracks, etc. Then calculate the total room volume and apply basic gas laws- %-age of excess volume supplied times ambient atmospheric pressure yields likely room pressure. 110% of volume supplied is actually 2.5% of volume excess supply with the 75% loss which will yield a 2.5% pressurization calculated at (102.5% / 100%) times atmospheric pressure, or 0.025 x 360 inches WC => 9 inches WC pressurization.

Example- assume a 30 x 50 x 12 foot room = 18000 Cu Ft. Assume 20 air changes per hour design turnover => 6000 CFM supply and exhaust air.

Assume that the desired positive pressure is 0.25 inches WC. If the desired pressure was 30 feet WC (or 360 inches WC), the required excess air supply would have to be 100% (360 inches WC / 360 inches WC) times 18000 or 18000 Cu Ft per minute over normal supply and exhaust volumes. 0.25 inches WC is 0.000944 of atmospheric pressure (0.25 inches WC / (30 feet WC x 12 inches per foot)). Therefore, the NET pressurization supply to support 0.25 inches of WC pressure should be 0.000694 times the room volume or 13 CFM over design supply. Using the 75% lost factor, the excess supply volume should be 13 / (1-75%) or 52 CFM excess supply.

Using our example, the 20 AC per hour requires 6000 CFM supply and exhaust, so we should supply 6052 CFM and exhaust / return 6000 CFM. A safe condition would be to supply 6000 + (up to 10 times the calculated 52) CFM using a variable speed drive set to maintain defined pressure boost over ambient, or 6520 CFM maximum supply capacity and a 6000 CFM exhaust / return volume.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#5
In reply to #3

Re: Positive air pressure calculations in a room

06/08/2010 2:09 AM

You are correct for 'rule of thumb' but İ am not certain about the rule of 'thump'. Makes me think they have a bouncer to take care of anyone causing a pressure loss.

Register to Reply Off Topic (Score 5)
Participant

Join Date: Sep 2012
Posts: 4
#10
In reply to #3

Re: Positive air pressure calculations in a room

09/11/2012 1:38 AM

you just saved my life....hats off boss!

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#11
In reply to #10

Re: Positive air pressure calculations in a room

09/12/2012 1:06 PM

Sounds to me like energygod deserves a GA vote!

I will do the customary thing and hit the 'Rate' button in his post #3, and then vote "Good Answer".

__________________
Semper Ubi Sub Ubi
Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#12
In reply to #3

Re: Positive air pressure calculations in a room

03/22/2015 9:29 PM

Why are you dividing 0.25"W.C./360"W.C.?

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#13
In reply to #12

Re: Positive air pressure calculations in a room

03/22/2015 11:14 PM

That is to determine the RATIO of the desired over-pressurization compared to "standard" ambient (sea level) air pressure- which using "American" terms is about 30 feet water pressure (or 30 x 12 inches per foot = 360 inches).

The 0.25" water column (WC) pressurization requires (0.25 / 360) of excess air, or 0.006944 times the equilibrium value. This is based on gas laws relating pressure to air volumes (which is a direct ratio). 1" of excess pressure would require (1 / 360) times base volume as excess air supply.

Another way to calculate it is to compare the required NET pressure vs. base pressure, or (360.25 / 360) times the equilibrium supply air volume for total required supply air BUT the original way gives you a SPECIFIC VALUE for excess air which you can easily "bump" to provide a safety factor potential (which is why you use a VFD on the supply fan sized for the safety factor amount added to the equilibrium amount- allowing the fan to supply as much excess air as is needed to meet the required over-pressure setting.

Hope this helps. If not, send in a another reply to this note.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#14
In reply to #13

Re: Positive air pressure calculations in a room

03/23/2015 1:55 PM

30 feet being an approximation of 14.7psi x2.31=33.957 feet?

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#15
In reply to #14

Re: Positive air pressure calculations in a room

03/23/2015 2:47 PM

That is correct- I used a short cut with my discussion.

Obviously, you should use the pressure for your elevation as the basis.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Participant

Join Date: Mar 2015
Posts: 3
#16
In reply to #3

Re: Positive air pressure calculations in a room

03/23/2015 9:10 PM

Shouldn't we be taking leakage into account using Q (CFM) = 2610 x A (ft2) x (DP)^0.5 ? Also, i would know how to calculate this area for say a door crack but what would you assume for leakage through the construction?

Register to Reply
Commentator

Join Date: Jul 2009
Location: italy
Posts: 58
Good Answers: 6
#4

Re: Positive Air Pressure Calculations in a Room

06/08/2010 12:35 AM

I agree with all the theory, but from a practical point of view I would:-

  1. First establish how much air you want to circulate. This depends on the volume of the room and the law requirements.
  2. Install two identical ventilators of the required volume, one for input air and one exhaust.
  3. Apply a motorized damper on the exhaust ventilator
  4. Use a sensitive pressure gauge (two for more precision ) and with a simple electrical circuit you can control the damper and consequently the pressure in the environment.

I did not exactly answer your question but the result is what counts.

Register to Reply Off Topic (Score 4)
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#6

Re: Positive Air Pressure Calculations in a Room

06/08/2010 10:52 AM

Start by calculating the CFM of outside air required by your local code, based on occupancy and usage of the space: clean room, laboratory, operating room, etc. Design the exhaust system to handle that same quantity of air. Theoretically this will give you zero space pressure difference referenced to the adjacent spaces. Equip the exhaust fan with a variable frequency drive (VFD) and slow the fan speed to arrive at the pressurization desired...usually 0.05 to 0.10 will do the trick. Employing the services of a professional balancing firm is recommended followed by a thorough commissioning process to assure that the design parameters have been met. That good start should be followed by a competently designed and executed, on-going maintenance program. The occupants of this space can now concentrate solely on carrying out the mission for which the space was designed and built.

Register to Reply
Active Contributor

Join Date: Jun 2010
Location: Chennai India
Posts: 20
#7

Re: Positive Air Pressure Calculations in a Room

06/10/2010 5:43 AM

determine the air leakages through the door and crevices etc and then decide the air changes required and always exhaust slightly less than the supply air to ensure pressurization is maintained.

Methodolgy is available in the book "design of clean rooms".

__________________
enervac
Register to Reply
Guru

Join Date: Nov 2009
Location: Izmir, Turkey
Posts: 2142
Good Answers: 31
#8
In reply to #7

Re: Positive Air Pressure Calculations in a Room

06/10/2010 8:55 AM

Doing anything is being silly. You have to learn the losses in order to proceed.

Register to Reply
Commentator

Join Date: Jul 2009
Location: italy
Posts: 58
Good Answers: 6
#9
In reply to #7

Re: Positive Air Pressure Calculations in a Room

06/10/2010 11:19 AM

Presuming that you know how much of air you want to circulate in the room and how much positive pressure you need, you have only two known data.

Your variables are the air " leakages through the door and crevices" which can be roughly calculated however doors opening and closing which cannot be controlled.

Using a variable speed fan as indicated by " Lou Bindner" can be a solution if you do not require a precise positive pressure because frequent door openings will unbalance the system.(There is also the efficiency graphic to be considered)

An automatic damper controlled by a pressure gauge as I have earlier indicated in # 4 will solve your problem. It has been working in a hospital in my home town since 25 years.

Register to Reply
Commentator

Join Date: Jul 2008
Posts: 63
#17

Re: Positive Air Pressure Calculations in a Room

07/05/2015 1:46 AM

Forget about leakage etc. Have a Pressure difference control set with 20 pascals set pressure for conditioned room and interface it with your BMS with audio and video annunciation so that you will be alerted the moment the inside pressure drops below the minimum set pressure to take remedial action

Register to Reply
Active Contributor

Join Date: Jun 2010
Location: Chennai India
Posts: 20
#18
In reply to #17

Re: Positive Air Pressure Calculations in a Room

07/07/2015 9:49 PM

The actual measurement of pressure difference can take place after the design installation.If the design does not take care of the leakages and other requirements you may have to start from the begining.

__________________
enervac
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

angelo (2); Doorman (1); energygod (3); enervac (2); Lou Bindner (1); Markmark (3); Padmanabhan Iyer (2); russ123 (2); tanveer.aziz (1); user-deleted-1105 (1)

Previous in Forum: Bearing Material Calculation   Next in Forum: Pump Designing

Advertisement