I have a query regarding the settings of I>, I>> (over current protection) of one distribution feeder.
Problem:
CT rating :300/1A
Settings of I> :
Current setting I> : 1A
Time setting(sec) : 0.2Sec
Characteristics : IDMT NI
Settings of I>> :
Current setting I>> :4A
Time setting(Sec) : 0.3sec
Characteristics : DMT
Areva Micom P111 relay is used here and these are the settings set in the relay.
At First, are these settings correct and coordination is proper ?
My actual query :
If 3-ph fault would happen and its fault current is about 1000A(case-1) and 2000A(case-2)
Then what protection I> or I>> will pick up and give the trip command?
My Assertion :
Im thinking that If the fault current is lessthan 300x4=1200A( I>> setting) , I> will follow the Inverse characterstic and accordingly fault will be clear in less than 0.2sec.
If the fault current is more than or equal to I>> setting, I>> will be picked up first as it is DMT and give the tripping command with allocated the time delay and I> never picked up .
Is my assertion correct?
Good Answers: