There are Start /Stop Commands Generated From DCS going to MCC, For Digital Output Module which Type of scheme is most Recomended and safe type ,

1) Like I have the Option either to Use Relay Contact Module (Potential Free ) or

2) 24 VDC Output Module with Interposing Relay after Output Module

Regards

Jose

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Selecting Digital Output Module

06/08/2010 1:15 PM

2) 24 VDC Output Module with Interposing Relay after Output Module

I always recommend isolating your I/O with a relay anyway.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#2

Re: Selecting Digital Output Module

06/09/2010 10:51 PM

Guest,

Both are frequently used. My choice would depend on a number of factors:

  • Availability of DC for controlling the contactors in the MCC.
  • Speed of response--AC has an inherently slower response than DC.
  • Ability to isolate the DC from higher-voltage AC signals.
  • Number of operations expected during the life of the equipment (solid-state devices are much more long-lived).

I would always design in certain components:

  • Surge suppression to eliminate or trap the voltage spikes from the contactor and relay coils so they do not damage the output module--diodes backwards for DC outputs and RC networks for AC outputs. Do this for relays or solid-state outputs.
  • Separate wireways as needed to conductors with different voltages apart.
  • Isolating relays being mandatory for certain types of loads such as horns or buzzers.
  • Hard-wired emergency stop circuits and wiring the power for the outputs through the master control relay.

--JMM

Reply
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#3

Re: Selecting Digital Output Module

06/12/2010 1:23 AM

Thanks for all the Info.

Regards

Jose

Reply
Reply to Forum Thread 3 comments
Copy to Clipboard

Users who posted comments:

jmueller (1); josej (1); RDGRNR (1)

Previous in Forum: Profibus   Next in Forum: DP Type LT

Advertisement