The High side of the D/P transmitter should be connected to the bottom tap and the Low side to the top tap.
There is some exemptions in one of our units the D/P's measuring levels are connected "backwards" in other words the Low side is connected to the bottom and the High side is connected to the top.
Thank you
__________________
"The older I get -The better I was"
The important point is know how the differencial pressure is going with the level rise, I mean, If you use wet leg configuration and the low side is ubicated in the bottom tap the ranges values be ubicated in the positives values like e.g: 1000mmH20 to 300mmH20, and If the high side is ubicated in the bottom tap the ranges values be ubicated in the negatives values like e.g: -1000mmH20 to -300mmH20.