Anonymous Poster

Earthing Resistance

06/09/2010 10:04 AM

How do you decide, if the earthing resistance should be less than 1 ohm? Why not 5,10,20 ohm. Can you explain.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Earthing Resistance

06/09/2010 10:28 AM

Any resistance with a current flowing thru it, have an inherent (and proportional)voltage drop across itself. And you want to minimize the potential difference between ground and the grounded device.

Yahlasit

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Earthing Resistance

06/09/2010 2:49 PM

The limiting values of maximum earth resistance are clearly indicated in whatever standard (be it building or equipment) you are working to and depend on the equipment and application. As for the decision behind how these limits were chosen in the first place, it all has to do with minimising the risk to people and property while at the same time making it practical (and economical) for builders and product designers to meet these limits.

__________________
jack of all trades
Reply
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Earthing Resistance

06/10/2010 9:58 AM

Who said that the Earthing System Resistance "SHOULD BE" less than one Ohm? As far as I know, no standard, I repeat, no standard - National or International - has anywhere specied a statutory maximum value to be maintained for Earthing System Resistance. If anybody demands so from you, please ask them to quote from any such Standards.

The more important factor is that the earth resistnace should be "low" enough as to cause a significant current flow during an earth fault so that the protective devices can operate to isolate teh fault quickly before it causes harm to the operating personnel and/or to the installation. As long as you can establish the above requirement, the absolute value of earth resistance does not matter at all.

Reply Good Answer (Score 3)
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#4
In reply to #3

Re: Earthing Resistance

06/10/2010 10:41 AM

"As far as I know, no standard, I repeat, no standard - National or International - has anywhere specied a statutory maximum value to be maintained for Earthing System Resistance"

The Ontario Electrical Safety Code does not give a specific value, but does say that the value should be low enough to limit potential rise of any grounded equipment to 5000 volts, (rule 36-304), this section of the Code deals specifically with installations over 750 volts. Depending on available short circuit current, this could require the resistance to ground to be less than 1 ohm.

Reply Score 1 for Good Answer
Anonymous Poster
#6
In reply to #4

Re: Earthing Resistance

06/10/2010 5:48 PM

I have to respond to the comments listed and make sure the facts are correct. I am a master electrician, master inspector and MSHA certified for low medium and high voltage. In the 2008 NEC code book ART. 250.56- if the resistance of a single grounding rod is over 25 ohms is shall be augmentd by an additional ground rod. In mining for substation locations 2 ground fields are required. 1 for the grounded conductor and 1 for the grounding conductor. Both ground fields are

limited to only a few ohms of resistance

Reply
Active Contributor

Join Date: Apr 2010
Location: 20 miles north of Mt. Shasta California along I-5...aka , Yreka, California.
Posts: 18
#5

Re: Earthing Resistance

06/10/2010 2:54 PM

Your question caught my eye because I compiled data on electrical differences between strata and distant locations up to a kilometer. This was to study the geochemical activity in an area of Northern California. But accuracy was lacking due to the various sources of these differences was skewed seasonally, thermally, time of day, moon position (affecting water flows in mountain tributaries) cloud motion and traffic all affected the results. To help reign in these oddities I sought to find a site that was most solidly connected to the rest of the planet and choose a site where lightening had struck more often than the nearby countryside for my study.

I decided to quit this project after my gear was destroyed by lightening three times in a month.

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); baxterm (1); electricalexpert65 (1); jack of all trades (1); robertgrist (1)