Anonymous Poster

Circuit Breaker

06/11/2010 11:48 AM

Why making capacity of a circuit breaker is always higher than breaking capacity?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Breaker

06/11/2010 12:09 PM
  1. Making capacity is a PEAK value while breaking capacity is an RMS value.
  2. There is a DC component as seen in this wave...

Please study IEC 60947-2. You will find it illuminating and interesting.

Good luck.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Breaker

06/11/2010 9:51 PM

While making on to a short-circuit, a breaker experiences electro-dynamic stress which is proportional to the square of the peak short circuit current. As you are aware, even in a pure sinusoidal AC Wave Form, the peak value is 1.414 times the R.M.S. value. Add to it, the DC component in the short circuit current, due to the stored energy is the system recatances, the peak value of the short circuit current further increases. Hence, the making capacity of a circuit breaker is always higher than the breaking capacity.

Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #2

Re: Breaker

06/11/2010 11:20 PM

why does the peak value plus dc components not applicable to breaking??

Reply
3
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: Breaker

06/13/2010 10:45 PM

(I have answered it in one of the previous threads. For convenience, it is pasted here)

To answer this question, let's first describe couple of concepts:

Breaking Current – The r.m.s value of the current at the instant of the contact separation is called the breaking current of the circuit breaker and it is expressed in kA.

Making Current: The peak value of the current at the time of making the contact of circuit breaker is called making current and it is expressed in kA.

Nature of Short Circuit Current: Over the time, the short circuit current goes with different state – (a) first 2 or 3 cycles is called sub-transient state, (b) next few cycles is transient state, (b) finally the steady state.

Generally, the short circuit current in sub-transient state is 1.8 to 2 times more than that of the steady state.

Circuit Breaker Fault Clearing Time: The circuit breaker has its fault clearing time which is the time elapsed between the instant of instance of fault occurrence and the instant of contact separation with final current zero.

Because of this time, actual contact separation of the circuit breaker occurs at time when the fault current reaches at its steady state. So, the breaking current of a circuit breaker considers the r.m.s value of the steady state of fault current.

Breaking current = r.m.s value of the steady state fault current

But, if a fault pre-exists and the circuit breaker is closed at this condition, the circuit breaker makes the contact with the fault current at the sub-transient state (or at best transient state).

Making current = The peak value of the sub-transient state fault current

= √2 x r.m.s value of the sub-transient state fault current

= √2 x 1.8 x r.m.s value of the steady state fault current

= 2.5 x r.m.s value of the steady state fault current

= 2.5 x Breaking current

So, the making current is almost 2.5 time of the breaking current.

Hope it helps.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 3)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Breaker

06/14/2010 12:37 AM

Dear msamad, (others are welcome too)

i would be grateful if you can visit my thread

http://cr4.globalspec.com/thread/54286

i am sure top switchgear companies are working on such software and may even have their own, but i haven't come across a commercially available one.. would welcome your views.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); kvsridhar (2); msamad (1)

Previous in Forum: Electric Terminal   Next in Forum: Three Phase Motor Protection Circuit

Advertisement