We have one tall column of 41 Meter Hight and two dia meter of 2.2 and 3.5 meter.
We are facing deflection at the top of column. So what will be the limit for allowable diflection at top.
Which code say about the permissible limit of deflection at top of column?
Re: Column
06/13/2010 8:18 AM
What country are you in?
CARPE CRUSTULORUM!
Re: Column
06/13/2010 8:32 AM
We are in Saudi Arabia ?
Good Answers: 114
Re: Column
06/13/2010 8:20 AM
What are these columns, are they refinery vessels? chimneys? Which country's codes do you use?
Re: Column
06/13/2010 8:33 AM
This column is Solvent Recovery column in our Benzene tolune xylene plant at saudi arabia
Good Answers: 61
Re: Column
06/13/2010 9:11 AM
Is the "Deflection" the result of thermal expansion on one side of the column due to solar radiation?
If so, have you thought about adding "Insulation with a Reflective Cover"?
Do it once and do it right
Good Answers: 74
Re: Column Deflection
06/13/2010 2:30 PM
The Canadian Institute of Steel Construction, CISC recommends h/400 for buildings. In your case, that would be 102 mm lateral deflection but if the connected material is sensitive to large deformations, you may wish to reduce that to a more acceptable value.
Bruce