Capacitor Rating with Single Phase Motor

06/13/2010 12:21 PM

how will you design capacitor rating of single phase motor

for power factor improvement?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#1

Re: Capacitor Rating with Single Phase Motor

06/13/2010 1:14 PM

From what I understand, the run capacitor rating on a capacitor-run type single phase motor is determined using algebraic phasor calculations.

This has been covered by a previous post: http://cr4.globalspec.com/thread/15299/Power-factor-correction-capacitor-for-Single-Phase-and-FHP-motors

__________________
CRTL-Z
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#2

Re: Capacitor Rating with Single Phase Motor

06/14/2010 3:57 AM

Normally power factor of capacitor start single phase motors is much improved. Any how, for calculating the desired capacitor, follow the link;

http://cr4.globalspec.com/thread/53635/How-to-Calculate-Capacitor-Required-to-Compensate-Given-KVAR

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Capacitor Rating with Single Phase Motor

06/14/2010 10:11 AM

Capacitor provided in a single-phase motor is definitely not for imroving power factor, but to provide a split-phase to make the motor self-starting. It could be a Capacitor-start motor or a Permanent Capacitor Motor. Values of Capacitors will vary for Start Capacitor & Run capacitor.

The criteria for selection would be sufficient torque development only to over come the static inertia of the motor & the connected load.

One can refer to Electrical Machine Design by M.V. Deshpande.