Substation Battery Rack Grounding

06/14/2010 5:12 PM

We have two different schools on this subject:

One: Substation DC battery rack metals should be better without bonding/grounding to the substation ground grid, because during the fault the substation area elevate on potentials so the grounding may affect the battery functionality.

The 2nd one is that it is better to ground all metal structures to the grounding grid including the battery rack, so create equi-potential for safety.

Currently in our utility the DC battery rack have not been bonded or grounded, is there any advice?

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#1

Re: Substation Battery Rack Grounding

06/16/2010 3:07 AM

Not working in a utility, I've never seen metal battery racks! Our traction substations (3kV DC electrified railways) use strong wooden racks for our 110V battery systems, and earth separation are regularly monitored. In our case, it is important to have very effective separation from earth, as there could be fairly large traction DC return currents flowing through earth under fault conditions. I can see that utilities could be different.

Reply
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#2

Re: Substation Battery Rack Grounding

06/16/2010 11:16 AM

Outstanding answer, CJ. You nailed all the relevant points in clear language.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#3

Re: Substation Battery Rack Grounding

06/17/2010 2:15 AM

The IEE Regulation is very specific on this issue by saying ALL METAL SHEETS should be properly bonded to earth. Bonding of the battery rack is a very necessary safety measure to prevent electrocution. So do the bonding, a regulatory body have asked U to do so and it has been proved right by all of us in Electrical Section of CR4.

Secondly, if the negative terminal of the battery is bonded to the rack, the rack should be separately earthed and not through the sub station ground grid. Ur fear of ONE, will occur if done other wise.

Dickson.

__________________
There is peace in silence and achievement in plans.
Reply
Anonymous Poster
#4

Re: Substation Battery Rack Grounding

10/23/2010 11:10 AM

Very nice explanation. Have you any experiences from Nuclear power plant about grounding battery racks? One guy are still saying that it is not necessary because racks are itself connected to the anchor plate, beucase we have thick layer of epoxy paint...is this sentences relevant for removing grounding from battery racks? ANd floor must be coated with anti-acid paint only or anti-static / insulated mat??? In Nuclear power plant you have IT system. thanks.

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#5
In reply to #4

Re: Substation Battery Rack Grounding

11/03/2010 2:53 AM

Dear GUEST,

In response, I have no special personal experience related to nuclear power plants.

You can generally rely on the accepted published standards, such as OSHA 1926.403-1986, but when it comes to something as sensitive as the implications of NUCLEAR power, the control, communication, IT and emergency systems and their power sources you can expected greatly increased caution, duplication, redundancy, anality and banality to the Nth degree.

This forum, at least my part in it, does not rise to that degree nor would I attempt it.

I can read however, and just completed several minutes of in depth review of several detailed reports, records, Standards etc on this subject. It's simply amazing what power lies in GOOGLE and de-classified documents.

Even with that availability, I would strongly recommend that you contact a few of the engineering companies engaged in the sales and engineering specifically geared toward NUCLEAR POWER installations. They were quite easy to find on the internet. I'm certain that what you have asked of us is not a state secret, and since it is safety related, I'm convinced they would gladly share some prepared materials they have available for public distribution on the subject of your question.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM